Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Data Center Expert stops registering data from netbotz 750

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Data Center Expert stops registering data from netbotz 750
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All
Related Products
product field
Schneider Electric
EcoStruxure™ IT Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Jorge_Carranza
Crewman Jorge_Carranza
Crewman

Posted: ‎2024-01-30 06:56 AM

1 Like
1
708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-30 06:56 AM

Data Center Expert stops registering data from netbotz 750

Hello EcoXperts.

 

I'm having an issue with Data Center Expert and a Netbotz 750 with one of our clients.

 

The system has been working for about 2 years now, and about a year and a half ago, they bought two Netbotz 750, for the monitoring of their Data Centers, and added them to DCE, a few months ago, they reported that one the Netbotz 750 was having connection issues.

 

Data Center Expert wasn't reporting anything unusual, but they noticed that the sensor data from the reports they were generating, had gaps in them of about half an hour each. Checking historical data for the appliance we noticed that this has been happening since a long time ago, occurring almost once every month for about thirty minutes.

 

Digging a little further in the stored data, we noticed that whenever this happens, it doesn't affect all the sensor every time.

 

The pictures attached were taken from the last two events that has occurred. 

 

All the other devices in Data Center Expert, work properly, it's just the netbotz 750 that show this issue; and whenever this happens, there is no active alarm of communication loss.

 

Thanks in advanced for the help.

 

Best regards

Attachments
Labels
  • Labels:
  • Data Center Expert
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2024-05-01 05:01 PM

0 Likes
0
563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-01 05:01 PM

Hi @Jorge_Carranza,

 

If this issue is still occurring I recommend reaching out to technical support to troubleshoot. They will work with you to gather all the needed details to analyze the situation and assist you and your customer through to a resolution of the issue.

 

If it is only certain sensors that are not getting values, but others are for a period of time that would likely explain why there is no communication lost issues within DCE as the device is still responding to some SNMP requests.

 

Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2024-05-01 05:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-01 05:01 PM

Hi @Jorge_Carranza,

 

If this issue is still occurring I recommend reaching out to technical support to troubleshoot. They will work with you to gather all the needed details to analyze the situation and assist you and your customer through to a resolution of the issue.

 

If it is only certain sensors that are not getting values, but others are for a period of time that would likely explain why there is no communication lost issues within DCE as the device is still responding to some SNMP requests.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of