EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:01 AM . Last Modified: β2024-04-04 01:13 AM
Hi,
Based on the experience, what is the maximun admitted latency between the DCE & DCO servers?
Thanks,
(CID:134035750)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:01 AM . Last Modified: β2024-04-04 01:13 AM
I was sure that somewhere there was a official document stating the latency requirements for DCE but have been unable to find it..
In my experience there is no fixed value for maximum latency. We have DCE servers that successfully monitor 100's of devices in different countries with ping response times of between 20ms and 450ms. The sites with higher latency have different scan settings in DCE.
I would say, (more from feeling than actual facts) that if you have a site with high latency and a large number of devices on that site then you may get spurious lost comms issues more often. Netbotz devices (not the 200/250) appear to be more susceptible to spurious lost comms.
We have one site with probably 300 devices and ping response of 200-300ms with no issues.
Not sure this is a definite answer but hope it helps..
(CID:134035970)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:01 AM . Last Modified: β2024-04-04 01:13 AM
I was sure that somewhere there was a official document stating the latency requirements for DCE but have been unable to find it..
In my experience there is no fixed value for maximum latency. We have DCE servers that successfully monitor 100's of devices in different countries with ping response times of between 20ms and 450ms. The sites with higher latency have different scan settings in DCE.
I would say, (more from feeling than actual facts) that if you have a site with high latency and a large number of devices on that site then you may get spurious lost comms issues more often. Netbotz devices (not the 200/250) appear to be more susceptible to spurious lost comms.
We have one site with probably 300 devices and ping response of 200-300ms with no issues.
Not sure this is a definite answer but hope it helps..
(CID:134035970)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:02 AM . Last Modified: β2024-04-04 01:13 AM
Thanks for the answer, it helps me a lot.
If someone has the official document link it would be great, since I was also looking for it without success.
(CID:134036002)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 12:02 AM . Last Modified: β2023-10-22 03:01 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.