I have an existing room and I can't access to it. Each time I try I get an error that shows "an exception error occured". What can be done to solve this issue?
(CID:94603065)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:19 AM . Last Modified: 2024-04-10 12:36 AM
Hi Tomestis, The first thing you could try is to remove the client files downloaded from the server. Removing those files will cause the application to re-download the files the next time you log in. The files are usually stored in C:\Users\< user>\.isxo\ You can delete the .isxo folder to force the client to download new files from the server. Please notice that the model on the server will not be influenced by the removing this folder. In case this doesn't resolve the problem please get back to us. We will then need to take a closer look at the client log files. Thanks Jesper
(CID:94603083)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:19 AM . Last Modified: 2024-04-10 12:36 AM
Tomestis,
this has been answered here and we have now verified the patch to fix this issue.
Richard Crowe
(CID:94603146)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:19 AM . Last Modified: 2023-10-31 11:11 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of