Is there a way to have cooling (CFD) be truly dynamic in DCO ?
I have no end of trouble getting DCO to show a reasonable representation of reality with regards to cooling.
It seems as if the whole system relies upon staticly configured manual entries.
ie: cabinet is presumed to pass X cfm per kW
However, I have cabinets with exhaust fans in the chimneys - and the fans are metered, and in the system - DCO should use the real time data
Additionally - I have set the CFM of my CRAC units - I would expect the system to understand that the CRAC units CFM should equal the discharge from your supply tiles , perhaps minus some percentage for leakage... but that doesn't seem to be the case,
In my case - the presumption of the cabinets air flow is massively imbalanced compared to the CRAC units known air flow -
am I just missing some switch that says - "make this work like reality" or something ?
(CID:132669922)
- Labels:
-
Data Center Operation
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:58 PM . Last Modified: 2024-04-04 04:00 AM
Hi Eric,
I would try using/associating some temperature sensors, and then running the 3D view based on "Measured plane":
that may provide us more realistic simulation of the temperature map.
Kind regards
(CID:133370561)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:58 PM . Last Modified: 2023-10-22 02:50 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.