Is it possible to connect a AP9512TBLK to a Netbotz 320E?
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-0211:58 AM. Last Modified: β2024-04-1012:01 AM
Hi Graham
The 320E is a version 2 device so Version 3 sensors are not compatible, the TS100 is the temperature sensor, HS100 Humidity sensor, FD100 Fluid sensor. There are also Dry contact sensors and 0-5v sensors.