Installing Multi-Tech MultiModem cell on NB 450

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Installing Multi-Tech MultiModem cell on NB 450
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:57 AM . Last Modified: ‎2024-04-10 01:03 AM

0 Likes
10
1367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:57 AM . Last Modified: ‎2024-04-10 01:03 AM

Installing Multi-Tech MultiModem cell on NB 450

Hi,

I have connected the USB cable of  Multi-Tech MultiModem cell (MTCBA-G2-U-ED) and seem not to be getting any success in the installation, after adding it as a Multi-Tech MultiModem cell in the serial devices.

Kindly find the below appliance log and advise how well I can get this installed.

 

Regards,

Felix

(CID:93913560)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

0 Likes
0
1367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

Hi Felix!

What version of firmware installed on Netbotz appliance?

There is an issue with modems on 4.4, which should be fixed in next release.

You could try to downgrade Netbotz to 4.3 version and it should work fine.

(CID:93913562)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

0 Likes
0
1367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

Hi Kozlov,

 

Thank you, I have done exactly just that and am seeing some progress as shown below on the status tab of the SMS configuration. 

 

However, I am not able to sent SMS alerts, please find the appliance log below and kindly advise.

(CID:93913580)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

0 Likes
1
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

Hi kozlov,

I have solved the issue, now the sms alerts are coming.

Thank you for your support.

Regards,

Felix

(CID:93913588)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

In response to DCIM_Support
0 Likes
0
1367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

Hi! Glad to help you!

(CID:93913855)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

0 Likes
0
1367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

Hello, i have the same issue with Netbotz 455, firmware is latest: 4.5.0. My modem is MTCBA-G2-U.

If this issue is not solved in 4.5.0, how i can downgrade it?

 

Thank you.

(CID:99158053)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

0 Likes
2
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

HI Cemil!

To downgrade, you need to donwload proper version of firmware from apc.com.

In that archive you can find tftp folder, which contain all necessary files to upgrade/downgrade. How to do this described in readme file in same folder.

(CID:99158136)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

In response to DCIM_Support
0 Likes
0
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

Hi Valentin Kozlov,

I'm interested in the downgrade procedure for the NetBotz appliance firmware from version 4.6.1 to the version, for example, 4.3 and below. Your link to the necessary software and downgrade information is no longer valid. Can you help me or already need to contact only local support?

Very thanks for the support.

(CID:123345409)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

In response to DCIM_Support
0 Likes
0
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

I found this instruction FA176133 for the downgrade procedure, but it says that it is applicable to NetBotz version 3. Therefore, I have a question: can this procedure be used for NetBotz version 4?

Very thanks for the support.

(CID:123345411)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

0 Likes
0
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:58 AM . Last Modified: ‎2024-04-10 01:03 AM

Hi Guys I have just logged in here after struggling onsite to get the same config going as Felix. Netbotz 450 4.5 > MTCBA-G2-U-ED. Is it still the recommendation to downgrade to 4.3 from 4.5 and give 4.4 a miss ?

(CID:103586237)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:59 AM . Last Modified: ‎2023-10-31 11:10 PM

0 Likes
0
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:59 AM . Last Modified: ‎2023-10-31 11:10 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore