EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:47 AM . Last Modified: 2024-04-05 04:27 AM
HELLO I TRY TO ACCESS TO MY DCO CLIENT BUT GENERATE THIS ERROR:
IMPOSSIBLE TO VALIDATE USER CREDENTIALS. SEE THE DETAILS OF
REGISTRATION OF THE APPLICATION
I´M VALIDATE AN ALL SERVICES ARE RUNNING
(CID:126165068)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:48 AM . Last Modified: 2024-04-05 04:27 AM
CURRENT VERSION 8.1
(CID:126165244)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:48 AM . Last Modified: 2024-04-05 04:27 AM
Hi Omar,
It seems you are trying to connect via port 80, but DCO configured to respond using SSL connection (via port 443). You can select the SSL connection in Advanced Settings:
Kind regards
(CID:126165248)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:48 AM . Last Modified: 2023-10-22 02:39 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.