How to reset the Rack monitor 570

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How to reset the Rack monitor 570
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:15 PM . Last Modified: ‎2024-04-04 03:24 AM

0 Likes
10
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:15 PM . Last Modified: ‎2024-04-04 03:24 AM

How to reset the Rack monitor 570

(CID:134022907)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:15 PM . Last Modified: ‎2024-04-04 03:23 AM

0 Likes
5
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:15 PM . Last Modified: ‎2024-04-04 03:23 AM

Dear Shoaib Maqsood,

If you mean reset NetBotz-4.x appliance to the default login values, then according NetBotz Rack Monitor 450/550/570 Installation and Quick Configuration Manual you need:

I hope this is what you need.

With respect.

(CID:134022919)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:15 PM . Last Modified: ‎2024-04-04 03:23 AM

In response to DCIM_Support
0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:15 PM . Last Modified: ‎2024-04-04 03:23 AM

Hello dear,

I  want to factory default the Rack monitor . Because i can,t access the rack monitor through network or console port .

(CID:134022947)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

In response to DCIM_Support
0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

Dear Shoaib Maqsood,

Then the above instruction is what you need.

However, you still need to serial connect your laptop/PC to the console port NetBotz-4.x appliance in accordance with the instructions:

With respect.

(CID:134022955)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

In response to DCIM_Support
0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

 

what did you mean by ( step 1 ) .

(Connect USB A to USB mini B cable to the console port on Netbotz Appliance)

 

(CID:134023016)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

In response to DCIM_Support
0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

This is 5-m (16.4-ft) USB cable included with your NetBotz-4.x appliance.

(CID:134023031)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

In response to DCIM_Support
0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

Hello Dear,

I have a rack monitor 570. After applying this procedure it stop on a starting boot services. On other side when we connect this rack monitor with advance view utility it stop on this step.  Image is attached for your kind reference. 

(CID:136152978)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

Hello Shoaib, please check this link: http://www.apc.com/nl/en/faqs/index?page=content&id=FA158175

(CID:134023009)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

Dear Shoaib, 

If the Netbotz is still reachable via a web browser, you can do the same by accessing the page below

http:// 

Once the appropriate credentials are provided, it will bring up a message saying that the restart has been initiated.

Otherwise, you can do issue the configreset command after establishing a terminal emulation (HyperTerminal) session to the Netbotz appliance after following the instructions laid out in one of Spezialist's comments.

 

I hope this helps.

 

Kind regards,

 

Justine

 

(CID:134023213)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2024-04-04 03:23 AM

Dear Shoaib Maqsood,

Tell us, please, have you solved this question or not?

With respect.

(CID:134026450)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2023-10-22 02:34 AM

0 Likes
0
1961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:16 PM . Last Modified: ‎2023-10-22 02:34 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore