Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84571members
353844posts

How to fetch data from a third Party API to the DCE

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
Warne
Crewman
Crewman
0 Likes
5
1487

How to fetch data from a third Party API to the DCE

Hello,

 

Is there a way to integrate a third party API with the DCE? There are only few status to be monitored through this API. 

 

Thank you.

Tags (1)

Accepted Solutions
APC_Steve
Commander Commander
Commander
4
1461

Re: How to fetch data from a third Party API to the DCE

Hi @Warne ,

 

The API available through DCE is for monitoring DCE and it's devices. Your question however seems to be more related to DCE using an API to monitor a 3rd party device. Sorry but there is no option for this. DCE can monitor SNMP and modbus 3rd party devices. It does use an API to monitor NetBotz devices however that is a built-in functionality and not outwardly exposed for use with other systems.

 

Thanks,

Steve

See Answer In Context

Tags (1)
5 Replies 5
APC_Steve
Commander Commander
Commander
4
1462

Re: How to fetch data from a third Party API to the DCE

Hi @Warne ,

 

The API available through DCE is for monitoring DCE and it's devices. Your question however seems to be more related to DCE using an API to monitor a 3rd party device. Sorry but there is no option for this. DCE can monitor SNMP and modbus 3rd party devices. It does use an API to monitor NetBotz devices however that is a built-in functionality and not outwardly exposed for use with other systems.

 

Thanks,

Steve

Tags (1)
gunturhakim
Cadet
2
1443

Re: How to fetch data from a third Party API to the DCE

Hi Steve,

that true, DCE have own API
bandungbest regards

Tags (1)
APC_Steve
Commander Commander
Commander
1
1435

Re: How to fetch data from a third Party API to the DCE

hi @gunturhakim ,

I'm not sure if that's a question or statement but yes, that's true. If you need information, it can be found here:
https://dcimsupport.ecostruxureit.com/hc/en-us/sections/360006467394-DCE-web-services-API

 

Steve

Tags (1)
Gabriella
Cadet
0 Likes
0
1424

Re: How to fetch data from a third Party API to the DCE

I want to make a website, which will be a sort-of search engine. A user enters a search term in a text box, and that data will be sent to several third party API's as query. Because the API's of course don't return completely similar responses, the data has to be parsed.

 

 

 

 

 

Kroger Schedule

Tags (1)
Warne
Crewman
Crewman
0
1413

Re: How to fetch data from a third Party API to the DCE

Thanks Steve. 

Tags (1)