Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84653members
354001posts

How to add output capability to a Netbotz 355?

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
DCIM_Support
Picard
Picard
0 Likes
4
283

How to add output capability to a Netbotz 355?

This question was originally posted on DCIM Support by Luis Fernando Ruiz Herrera on 2016-01-15


Hi, I want to trigger an output remotely that will lock a door, through a NetBotz 355.

 

 

(CID:105460240)


Accepted Solutions
DCIM_Support
Picard
Picard
0 Likes
0
283

Re: How to add output capability to a Netbotz 355?

This answer was originally posted on DCIM Support by Steven Marchetti on 2016-01-19


Hi Luis,

 

If you were to use a NetBotz 450, that unit has a relay output on it already. From that you could simply wire it to a relay which could trigger your door open mechanism. If you go with the 455/456, you would need extra hardware. The quick config guideis here:

http://www.apcmedia.com/salestools/LSCZ-7DGMPF/LSCZ-7DGMPF_R4_EN.pdf?sdirect=true

This shows the Sealevel devices as I had previously mentioned, and which will work with the USB capable NetBotz appliance. This info is on page 28. The sealevel device could then be configured similarly to the output relay on the 450 unit to trigger the door mechanism.

 

There is also mention of a PDU. The older AP79xx units can be used but they must also have old firmware on them to work. The integration was based on PDU 2.7.4 firmware and interaction with the hyperterminal menu. The menu has subsequently changed so the older firmware is a must as per k-base FA158332.


Steve

(CID:105460499)

See Answer In Context

4 Replies 4
DCIM_Support
Picard
Picard
0 Likes
1
283

Re: How to add output capability to a Netbotz 355?

This answer was originally posted on DCIM Support by Steven Marchetti on 2016-01-15


Hi Luis,

 

That type of control is not available on the 355. Our rack access requires the 4xx or 5xx series NetBotz devices. Output based on a relay output or a connected Sealevel output device (also output relay)  also requires the 4xx and 5xx series units. The 355 simply does not have that capability.

 

Steve.

(CID:105460254)

DCIM_Support
Picard
Picard
0 Likes
0
283

Re: How to add output capability to a Netbotz 355?

This comment was originally posted on DCIM Support by Luis Fernando Ruiz Herrera on 2016-01-18


Thanks for the answer. So, if using a NetBotz 456 and a facility door (not a rack door), what else would I need to have an output that could close the door?

(CID:105460431)

DCIM_Support
Picard
Picard
0 Likes
0
284

Re: How to add output capability to a Netbotz 355?

This answer was originally posted on DCIM Support by Steven Marchetti on 2016-01-19


Hi Luis,

 

If you were to use a NetBotz 450, that unit has a relay output on it already. From that you could simply wire it to a relay which could trigger your door open mechanism. If you go with the 455/456, you would need extra hardware. The quick config guideis here:

http://www.apcmedia.com/salestools/LSCZ-7DGMPF/LSCZ-7DGMPF_R4_EN.pdf?sdirect=true

This shows the Sealevel devices as I had previously mentioned, and which will work with the USB capable NetBotz appliance. This info is on page 28. The sealevel device could then be configured similarly to the output relay on the 450 unit to trigger the door mechanism.

 

There is also mention of a PDU. The older AP79xx units can be used but they must also have old firmware on them to work. The integration was based on PDU 2.7.4 firmware and interaction with the hyperterminal menu. The menu has subsequently changed so the older firmware is a must as per k-base FA158332.


Steve

(CID:105460499)

DCIM_Support
Picard
Picard
0 Likes
0
283

🔒 Closed