How do I enable SSL communication between Struxureware Data Center Expert and multiple Netbotz devices?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How do I enable SSL communication between Struxureware Data Center Expert and multiple Netbotz devices?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2024-04-10 01:48 AM

0 Likes
3
701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2024-04-10 01:48 AM

How do I enable SSL communication between Struxureware Data Center Expert and multiple Netbotz devices?

SSL (HTTPs) is a more secure form of communication than the standard HTTP. More and more users employ the use of SSL (HTTPs) to reduce the likelihood of data loss and potential cyber attacks..

How can I enable SSL in StruxureWare DCE?

(CID:83656811)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2024-04-10 01:48 AM

0 Likes
1
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2024-04-10 01:48 AM

Struxureware Data Center Expert and Netbotz Communication

Struxureware Data Center Expert (DCE) can monitor numerous Netbotz devices through the use of HTTP or HTTPs, either by a periodic polling of each device or a POST received from any one Netbotz device. Information retrieved from each Netbotz unit may include alarm data, configuration data, or surveillance data. During the initial discovery process, the user can configure DCE to discover and monitor each Netbotz device through the use of HTTP or HTTPs. Once discovered, the IP address or Hostname of the DCE will be configured on each discovered Netbotz device. You can confirm these settings by accessing the Netbotz, through Advanced View, clicking on the Configuration Pane then the Infrastruxure Central icon located under Appliance Settings. The Netbotz device will now POST information to the DCE in the event of an alarm or other data. 

When discovered through HTTP, the IP address or Hostname will appear similar to the following: 192.168.1.1.
When discovered through HTTPs, the IP address or Hostname will appears similar to the following: 192.168.1.1:443. 

Changing a device discovered via HTTP to HTTPs

If a user has discovered numerous Netbotz devices via HTTP but is required to switch communication to HTTPs, the following steps should be followed. Make sure that HTTP and HTTPs are both enabled on the Netbotz. Through the DCE client, click on Device/Netbotz Appliance Configuration/Web Server Settings. All Netbotz devices, monitored by the DCE, should appear in the list. The HTTP and HTTPs settings should also be listed. Check all Netbotz devices that are being switched to HTTPs and click Next. On the next screen confirm that HTTP and HTTPs are checked, click Next. The last screen will show status information on all devices. Confirm that all devices are listed as Complete, then click Finish. Re-discover all Netbotz devices using HTTPs. 

If the DCE server has the original discovery saved to discover all Netbotz devices, edit the discovery. To edit the discovery, click on the Saved Discoveries tab via the DCE client. Highlight the discovery, then click on the Edit Discovery Settings icon, located in the right hand corner (the icon contains a pencil and pad of paper). Select the correct Security Mode option from the drop down menu (for SSL you will use either Try SSL, fall back to none; Require SSL, no certificate validation; Require SSL, validate certificates.) The Port Range field should automatically populate with the default number 443. Click Next. Confirm that the Netbotz will be in the correct Device Group. Click Next. Check Run Discovery Now and click Finish. The DCE should now discovery the Netbotz devices using HTTPs. 

If the discovery was not saved, a new discovery will be need to be created. Through the DCE client interface, click on Device/Add Device. You should now follow the same steps as outlined previously in editing the discovery. If all Netbotz devices are in the same IP range you can create one discovery for the range of Netbotz devices rather than creating a discovery for each and every Netbotz device. 

Once the discovery process is complete, the settings will need to be configured on each Netbotz device. Through the DCE client, click on Device/Netbotz Appliance Configuration/Post Alert Data Settings. Choose the IP address or Hostname to use under the "Select the address to use for sending alert data" menu. Click OK. 

Log into the Netbotz devices and confirm that the Infrastruxure Central icon is now populated with the IP address or Hostname of the DCE server with port 443. ex. 192.168.1.1: 443 

Assuming the settings have been configured you can now disable HTTP. Through the DCE client, click on Device/Netbotz Appliance Configuration/Web Server Settings. All Netbotz devices, monitored by the DCE, should appear in the list. The HTTP and HTTPs settings should also be listed. Check all Netbotz devices that are being switched to HTTPs and click Next. On the next screen uncheck HTTP but leave HTTPs checked, click Next. The last screen will show status information on all devices. Confirm that all devices are listed as Complete, then click Finish. 

Troubleshooting: 

If the HTTPs settings are not applied, please retrieve the server log (nbc.xml) from the DCE server and contact Netbotz technical support. Please also document the model number of each Netbotz unit and their firmware revision along with the DCE server and firmware information. The Netbotz model number and firmware information can be downloaded in a PDF report for easier troubleshooting. 

(CID:83656814)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2024-04-10 01:48 AM

In response to DCIM_Support
0 Likes
0
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2024-04-10 01:48 AM

Hi DCIM Support,

Excellent post: it must be placed in the TIPS AND IDEAS section.

With respect.

(CID:128758084)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2023-10-31 11:02 PM

0 Likes
0
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2023-10-31 11:02 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore