I want to reformat my Netbotz Appliance

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • I want to reformat my Netbotz Appliance
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:02 AM . Last Modified: ‎2024-04-10 01:48 AM

0 Likes
3
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:02 AM . Last Modified: ‎2024-04-10 01:48 AM

I want to reformat my Netbotz Appliance

I have both a Version 2 and 3 Netbotz Appliance that I want to reformat / factory reset. Could you let me know of the details? 

(CID:83656807)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:02 AM . Last Modified: ‎2024-04-10 01:48 AM

0 Likes
1
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:02 AM . Last Modified: ‎2024-04-10 01:48 AM

There are two methods to restore the factory default settings (including user ID and password) on a NetBotz V2/V3 300, 400, 500 series monitoring appliances. Keep in mind that ALL threshold and alert recipients will be reset using this process. 

 Method 1

How to restore the appliance to factory defaults if you know the admin username & password:

WARNING: When restoring the appliance to its factory defaults, only the appliance IP address, subnet mask, and default gateway settings are preserved. All other settings are reset to factory defaults by this procedure.

  1. Open a web browser
  2. Use the following url to reset everything except tcp/ip settings to defaults

http:///unconfig

  1. You will be prompted for an admin username password
  2. After it is entered, you will see a message on the web page that says the following:

Configuration reset requested (keeping basic network settings)....

Reset Initiated

  1. Close the browser
  2. The reset procedure is now complete, you will be able to log into the advanced view or basic (web) view with netbotz/netbotz

 

Method 2

How to restore the appliance to factory defaults if you do not know the admin username & password:

WARNING: All settings, including TCP/IP settings, are reset to factory defaults by this procedure.

  1. If you have a V2 appliance, use a null modem serial cable (included with the bot) to connect the appliance to your computer system. If you have a V3 appliance, use a USBA-USBB cable(included with the netbot) to connect the appliance to your computer system.
  2. Start a serial communications application (such as Hyper terminal) on your computer system.
  3. Configure and establish a serial connection with the appliance. Use the following serial communication settings:
    • Bits per second: 38400
    • Data bits: 8
    • Parity: none
    • Stop Bits: 1
    • Flow Control: Hardware
  4. After you have successfully established a serial connection to the appliance, power-cycle the appliance. When the message
  5. Hit any key to stop autoboot: 

    appears on screen, press Enter to interrupt the boot process and activate the NetBotz> prompt.

  6. Type at the NetBotz> prompt:  configreset  and then press Enter
  7. The appliance will erase its Flash memory, write a new default configuration, and then restart automatically.
  8. If you need to reset the appliance with a static ip, after the Netbot reboots, let it boot fully so that you get a login prompt.
  9. Login with either root/netbotz (V2) or root/apc (V3) and follow the prompts to reset the ip settings

You can now close the serial communications program, disconnect your console cable, and log into the appliance using the default User ID and Password of netbotz (V2) or apc (v3).

(CID:83656809)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2024-04-10 01:48 AM

In response to DCIM_Support
0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2024-04-10 01:48 AM

HI ,

It work after resetting but now i cannot get alarms i.e. smtp is not working from the device, FYI attach picture error msg.

Please advise..

(CID:137103830)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2023-10-31 11:19 PM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:03 AM . Last Modified: ‎2023-10-31 11:19 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore