I have many DC powered devices in my data centers that connect to BDFBs or BDCBBs in the room. DCO does not let me connect devices outside the cabinet. Please advise
(CID:128757269)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:17 PM . Last Modified: β2024-04-05 02:41 AM
Hi Shawn,
In general, in DCO, devices in a rack can only be powered from rack's available rack-pdu(s).
The usual power path in DCO is:
UPS -> PDU -> rack pdu -> "IT device"
and/or PDU -> rack pdu -> "IT device"
A possible workaround I could think of is adding & configuring some rack pdu(s) for those devices.
Kind regards
(CID:128757290)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:17 PM . Last Modified: β2024-04-05 02:41 AM
(CID:131958644)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:17 PM . Last Modified: β2024-04-05 02:41 AM
Hi Shawn,
I understand, but currently rack-mounted devices may only have power connections with rack-pdu(s) inside the rack. I can capture a feature request for you or you might want to post one here: Feature requests
Kind regards
(CID:131958833)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:17 PM . Last Modified: β2023-10-22 02:20 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.