EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:39 PM . Last Modified: β2024-04-08 12:54 AM
Asking on behalf of Rich:
Logging into Struxuware DCE 7.3.1 shows many devices reporting βthe device is offline due to login errorβ.
Please advise.
Thanks
(CID:117540725)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:39 PM . Last Modified: β2024-04-08 12:53 AM
Hi Stine, Rich,
If you've reset the device, make sure it's got the same IP and either change the user name and password DCE uses to log into the device or change the user name and password on the device to match that listed in DCE. You may want to also try re-discovering the device (not necessarily deleting it). You may also want to verify if the appliance had been using "post-only" mode. Make sure if you're set to communicate through SSL that both DCE and the appliance is set up properly. Make sure there's nothing between the bot and DCE blocking http/https communications and make sure there is nothing else using that IP that may cause a conflict.
If you need to speak with technical support directly, please check the "contact us" page under APC's support page for your specific region. Here's the example for the US:
http://www.apc.com/us/en/support/contact-us/index.jsp
Steve
(CID:117540765)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:39 PM . Last Modified: β2023-10-22 02:15 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.