Posted: β2020-07-02 11:27 AM . Last Modified: β2024-04-10 12:33 AM
Why Group's planned average mark value displayed on Tool tip is different from rack to rack in one capacity group and from configured average?
Example:
Group's average is 4.7 kW, for most of racks its displayed as 4.5 kw and at one rack it show 9 kW
In other Capacity Groups a have several values within group.
Could anyone explain this?
(CID:95354900)
Hi Valentin, Could you please post a screenshot of properties of the capacity groups you are having issues with? Please make sure that the advanced section is expanded in the screenshots. Regards, Torben
(CID:95354911)
Valentin Kozlov ?
(CID:95355128)
Posted: β2020-07-02 11:28 AM . Last Modified: β2024-04-10 12:33 AM
Here is Capacity Group properties:
(CID:95355154)
Hi Valentin, Thanks for posting the update. We'll look into this. Regards, Torben
(CID:95355156)
Hi Valentin,
As seen from the advanced phase configuration the average per phase is 4.5kW. This is the value shown in the UI tooltip.
The racks with 9kW is having 2 phases which each will provide 4.5kW.
The groups average load and the phase load is depended on each other and will when chanced influence one another. Reason for the 4.74 in group average planned is most likely that you have a number of racks in the group and some of these have more than 1 phase giving that the over all capacity available in the group in average is higher than the individual phase.
More information regarding capacity groups can be found Capacity Group Properties
(CID:95355396)
Posted: β2020-07-02 11:28 AM . Last Modified: β2023-10-31 11:00 PM
