Incorrect measured power values

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Incorrect measured power values
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:26 AM . Last Modified: ‎2024-04-10 12:33 AM

0 Likes
6
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:26 AM . Last Modified: ‎2024-04-10 12:33 AM

Incorrect measured power values

Hi All!

I have an issue with incorrect measured values displayed at Power overlay. Origin thread is here.

Calculated values was fixed, but DCO continues display measured rack load values greater than about half.

Some examples:

Is there any solution to fix this issue?

I've tried to re-associate devices, but with no luck.

I can't delete and re-discover PDUs in DCE as advised by Soren, 

Any ideas?

(CID:95354898)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • capacity
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:26 AM . Last Modified: ‎2024-04-10 12:33 AM

0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:26 AM . Last Modified: ‎2024-04-10 12:33 AM

Hi Valentin, Could you elaborate a bit on the devices that are showing wrongly in DCO. Which make and model are they? Are there any of the values reported in DCO that seems to be reported in DCE (looking in the device sensor list) Would it be possible to access the DCE server? This would be needed in order to understand the data reported from DCE in more detail by inspecting the DCE webservice interface.

(CID:95354947)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2024-04-10 12:33 AM

0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2024-04-10 12:33 AM

Hi Soren! There are APC AP7853 and AP8853 PDU's installed in racks. There is no such data in DCE sensor list, and values reported in DCO is about 1.5 times bigger than output power in DCE for inspected PDU's. It is not possible to access DCE server from Internet, but it's accessible locally. Today I found this link: http://dcimsupport.apc.com/display/public/UAOp74/Correcting+False+Power+Values+Reported+by+StruxureW... And it's seems that it's solution for our problem. But I have a question: Is it needed to upgrade DCE to version 7.2.6 before patch implementation? Now it is on 7.2.2 And in order to receive correct values we need: 1. Delete DCE from External Systems in DCO 2. Upgrade DCE to 7.2.6 3. Add DCE as External System and re-associate sensors with DCO objects.

(CID:95355066)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2024-04-10 12:33 AM

0 Likes
2
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2024-04-10 12:33 AM

Hi Valentin, Thanks for sharing the RMPDU types in use. As you mention you found the potential solution to the problem yourself. The patch will only work on v7.2.6 of DCE! (The mentioned DCE link in the page might be available on earlier versions 7.2.4+ however the functionality is not fully operational) The steps needed are 1. Upgrade DCE to 7.2.6 2. Apply patch to DCE 3. Wait for data in DCO to be adjusted. The data is adjusted over the 30 day period used in DCO for average/peak data. In general power data is stored for a year for report purpose so there the data will take longer to be corrected. Alternative 3. Remove the external system and reassociate devices in DCO. This will reset/delete all the power data and correct data will be seen shortly after (maybe a day is need to catch up on data from the last 30 days, depending on number of devices) So if it can be accepted the reassociation is not needed.

(CID:95355193)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2024-04-10 12:33 AM

In response to DCIM_Support
0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2024-04-10 12:33 AM

HI Søren! Did you know, is this patch included in new 7.2.7 release of DCE? Or we need to apply it when we upgrade to 7.2.6 and then upgrade to 7.2.7?

(CID:96763916)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2024-04-10 12:33 AM

In response to DCIM_Support
0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2024-04-10 12:33 AM

Hi Valentin, The patch it self is not included in v7.2.7 of DCE. The patch will however also work for 7.2.7 to my understanding. In v7.2.7 however there has been an update to the DDF handling these devices which should solve the problem seen. I would try upgrading to v7.2.7 and make sure the latest DDF is used for affected devices (might need rediscovery if DCE is upgraded). Otherwise once v7.2.7 is running I would apply the above patch to the system.

(CID:96764005)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2023-10-31 11:09 PM

0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:27 AM . Last Modified: ‎2023-10-31 11:09 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of