Galaxy VX enabled for 18 programable dry contact.

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
SESA380953
Ensign Ensign
Ensign
0 Likes
1
786

Galaxy VX enabled for 18 programable dry contact.

Hi Everyone:

 

By customer requirement we need to deploy GVX, enabled for 18 programmable dry contact. As I understand it is ready for 12 total (6 configurable). I know there is AP9810 for dry contact.

 

Could you give us a clue to get 18 total configurable, maybe a kind of hub to extend dry contact numbers. 

 

Thank you in advance.

Tags (1)

Accepted Solutions
tjlaw
Lieutenant Lieutenant
Lieutenant

Re: Galaxy VX enabled for 18 programable dry contact.

Hi, 

 

Just sharing my thoughts: 

 

1. 2 optional NMC + AP9810 and IO relay from UPS's IO Cabinet (6 programmable).

- Not sure if can support 2 x NMC with 2x AP9810?

 

2. Get a Modbus controller with programmable output relay. Modbus controller will poll the data from UPS and trigger 18 output relays. 

 

BR, 

 

TJ

 

 

See Answer In Context

Tags (1)
1 Reply 1
tjlaw
Lieutenant Lieutenant
Lieutenant

Re: Galaxy VX enabled for 18 programable dry contact.

Hi, 

 

Just sharing my thoughts: 

 

1. 2 optional NMC + AP9810 and IO relay from UPS's IO Cabinet (6 programmable).

- Not sure if can support 2 x NMC with 2x AP9810?

 

2. Get a Modbus controller with programmable output relay. Modbus controller will poll the data from UPS and trigger 18 output relays. 

 