Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:31 AM . Last Modified: 2024-04-08 03:30 AM
Hi Team ,
Our customer used Wiegand HID card which spec is 35bit 13.56MHz ,I'd like to know if this card can
support our APC HID rack access AP9361 ? I also check user manual but not sure it can work.
Kindly check it and would be appreciated .
Best Regards
(CID:110011387)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:31 AM . Last Modified: 2024-04-08 03:30 AM
HI!
AP 9631 works with HID cards and have antenna tuned on 125 KHz, So it's incompatible with 13.56 MHz cards.
As option you could look at Netbotz 250 with NBACS1356 handles. It supports 13.56 MIFARE cards and will support iCLASS cards soon.
(CID:110011440)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:31 AM . Last Modified: 2023-10-22 01:56 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.