After upgrading to 6.4.6 SNMP v3 is not working

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • After upgrading to 6.4.6 SNMP v3 is not working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:29 AM . Last Modified: ‎2024-04-08 03:31 AM

0 Likes
12
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:29 AM . Last Modified: ‎2024-04-08 03:31 AM

After upgrading to 6.4.6 SNMP v3 is not working

Upgraded a few APC management cards to 6.4.6 via SDCE. After the upgrade completes, SNMPv3 is not functional.

Detected an unauthorized user attempting to access the SNMPv3 interface from X.X.X.X.

 

This access worked perfectly before upgrading.

(CID:110011200)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

We need to know if this is true before performing upgrade on our as well...

(CID:110011535)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

Hi Zechariah Bauer, thanks for posting. Lets see who can be of assistance here. @community any ideas?

Kind regards Ditte   

(CID:110011646)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

Hi Zechariah Bauer, perhaps there's something in this question that can help you .

Cheers,

Stine

(CID:110013304)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

I upgraded my SDCE server to 7.4.2 and still have the same issue. When going from 6.4.0 to 6.4.6, my UPS's do not connect and they show the "Detected an unauthorized user attempting to access the SNMPv3 interface from X.X.X.X" error.

Even after verifying the SNMPv3 settings on both ends, the only way I have found to get the UPS to not show offline is to reboot the server.

(CID:110013386)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

0 Likes
4
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

Zechariah Bauer,

After upgrading a device to 6.4.6 and it reports lost communication, ensure that the device is fully upgraded using the web interface of the network management card.  Reboot the Data Center Expert server to see if the device recovers.

Please let me know if a reboot clears things up for that device.

Regards,

Cory

(CID:110013911)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

In response to DCIM_Support
0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

Cory McDonald Yes, rebooting the server is the only fix for this.

(CID:110013931)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

In response to DCIM_Support
0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

I've done three rounds of firmware upgrades with DCE 7.4.2 and each time required a reboot to clear false random loss of communication alarms.  This is obviously a bug.

(CID:110014248)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

In response to DCIM_Support
0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

Hello All,

This is an issue that is currently being looked into.  You can follow any updates in our knowledge base article.

http://www.apc.com/us/en/faqs/FA305661/

Regards,

Cory

(CID:110014720)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

In response to DCIM_Support
0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:30 AM . Last Modified: ‎2024-04-08 03:31 AM

Cory McDonald Is there any movement on this? That KB article has been the same past 20 days or so. This is frustrating to say the least.

 

-Zechariah

(CID:110791097)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:31 AM . Last Modified: ‎2024-04-08 03:31 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:31 AM . Last Modified: ‎2024-04-08 03:31 AM

This is a known issue .   More details in the link.  

http://www.apc.com/ie/en/faqs/index?page=content&id=FA305661&actp=search&viewlocale=en_US&searchid=1...

 

As for the error message "Detected an unauthorized user...", try updating your device definition files.  In DCE, select:

  • SNMP communcation settings,
  • device definition files,
  • add/Update definitions
  • SE StruxureWare ....

Alternatively, download the core.xml file from 

http://www.apc.com/ie/en/faqs/content/?id=FA303882

 

After that, reboot the DCE server.  

 

Good luck.

 

 

(CID:116362899)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:31 AM . Last Modified: ‎2024-04-08 03:30 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:31 AM . Last Modified: ‎2024-04-08 03:30 AM

Dear Zechariah Bauer,

Most recently, a new firmware v.6.5.2 was released for rPDU 2G.

As you can see from the short update description, the developers can to solve the above problem with SNMP v3:

At me, for example, updating by means of DCE software was successful.

Therefore, try it, and I hope this is what you need 😀.

With respect.

(CID:128747958)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:31 AM . Last Modified: ‎2023-10-20 05:00 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:31 AM . Last Modified: ‎2023-10-20 05:00 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of