Does Netbotz 570 is able to integrate third party sensors, such as thermostat ?
(CID:141267992)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:28 PM . Last Modified: 2024-04-03 02:59 AM
Hi Victor,
As spezialist eluded, we can work with some 3rd party sensors. The easiest of those use dry contacts. I would assume that's not what you're looking for with a thermostat so the other options to monitor them directly would be to use either a 0-5 volt connection or a 4-20 mA connection. You'd need to know the capabilities of the sensors or, if you've not yet purchased them, you'd want to consider these communications options if you want to integrate them to the NetBotz appliance.
On a side note, if you have sensors that are SNMP or Modbus compatible, you may also want to consider monitoring them directly through DCE.
Thanks,
Steve.
(CID:141268399)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:28 PM . Last Modified: 2024-04-03 02:59 AM
Dear Victor Juarez Velazquez,
The answer to this question depends on the 3rd party sensor (thermostat in your case).
Please specify which model and type of thermostat you want to connect to the NetBotz-570?
With respect.
(CID:141268161)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:28 PM . Last Modified: 2024-04-03 02:59 AM
Hi Victor,
As spezialist eluded, we can work with some 3rd party sensors. The easiest of those use dry contacts. I would assume that's not what you're looking for with a thermostat so the other options to monitor them directly would be to use either a 0-5 volt connection or a 4-20 mA connection. You'd need to know the capabilities of the sensors or, if you've not yet purchased them, you'd want to consider these communications options if you want to integrate them to the NetBotz appliance.
On a side note, if you have sensors that are SNMP or Modbus compatible, you may also want to consider monitoring them directly through DCE.
Thanks,
Steve.
(CID:141268399)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:28 PM . Last Modified: 2023-10-22 01:56 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.