EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:52 PM . Last Modified: 2024-04-04 02:44 AM
Why do I get "Detected an unauthorized user attempting to access the FTP interface " every day when a device (UPS) is polled by EcoStruxure IT?
(CID:134027314)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:52 PM . Last Modified: 2024-04-04 02:44 AM
Hi John,
The FTP credentials for that device don't match those in the Gateway. You can add the credentials for that device in the Device File Transfer Settings option in the Gateway. Here's some information from the Help Center you'll find useful: Configuring device file transfer settings and a troubleshooting article:I am getting unauthorized FTP access emails daily
Best regards,
Jackie
(CID:134027337)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:52 PM . Last Modified: 2024-04-04 02:44 AM
Yes they do match. I already had added the credentials for that device (UPS) in the Device File Transfer Settings option in the Gateway.
(CID:134027347)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:52 PM . Last Modified: 2024-04-04 02:44 AM
Hello John,
To dive deeper into Jackie's answer above. EcoStruxure IT not only requires the username and password for the NMC but we require the admins username and password. The network card restricts FTP rights to only the admin user and not another other user of the card. As well as, please confirm that the port numbers match as well. Those would be the two reasons that FTP is not working but based on the error I am leaning toward user rights or credentials.
Thank You
Victor
(CID:134027365)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:52 PM . Last Modified: 2024-04-04 02:44 AM
I was using 'apc' for the username and password. That is the factory default I believe and it is a User Type of 'Super User'. Or should I login with the username of 'Manager' that we created with the User Type of 'Administrator'?
(CID:134027421)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:52 PM . Last Modified: 2024-04-04 02:44 AM
Dear John Beck,
Tell us, please, did you solve your problem or not?
With respect.
(CID:134680051)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:52 PM . Last Modified: 2023-10-22 01:52 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.