NB250 dry contact sensors disconnects and connects again

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NB250 dry contact sensors disconnects and connects again
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

0 Likes
5
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

NB250 dry contact sensors disconnects and connects again

Hello

 

I replaced a clients NB200 with a NB250 2 months ago and connected all the old sensors on the same ports as the old Netbotz unit including two "Dry contact" sensors connected with the original NBES0304 cables. I added a few temperature sensors and wireless sensors as well.

 

A week ago I started to get "Dry contact sensor disconnected" alarms and a few seconds later the alarm cleared again. After a few minutes it repeats itself.

This happens on both of the dry contact sensor inputs so I can rule out an hardware error on the sensor cable itself or the device connected to the cables.

09/05/2018 15:56:57 Device NB: Sensor connected for 'XXX' at 'XXX'.

09/05/2018 15:56:54 Device NB: Sensor Disconnected for 'XXX' at 'XXX'.

the state of the sensor (open/closed) does not change, it just disconnects and disappears from the sensor list and appears a few seconds later.

 

So why does this occur?

The rj45 contacts are plugged in as they should be in the sensor ports.

I have done a soft restart of the NB250 but that did nothing.

Is this a firmware related error? the NB250 runs the latest 6,5,6 version and the wireless sensors connected runs the latest release as well.

The site is an unmanned site so there is no option to go to the site and do a hard reset every time this starts to occur.

 

(CID:134027597)

Labels
  • Labels:
  • NetBotz
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

Hi Adam lindberg, thanks for posting!

Let's hope you find your answer here.

Thanks,

Stine

(CID:134029002)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

0 Likes
2
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

Not sure if this is related, as this was a few years ago, but the symptoms sound similar. I had a NB200 that was doing similar things when using dry contact sensor.  But only if I have more than 3 dry contact sensors connected.  This happened on a replacement NB200 too.

I was informed at the time that this is a firmware issue, and to cut a long story short I ended up connecting a NB Pod 150 to the A-Link of the NB200 and connecting all the dry contact sensors to that..  The system has been running for a good few years since with no issues (as far as I know).

I suspect that the NB250 shares some firmware from the NB200 as there was a firmware update recently on the NB250 that addressed one of the bugs of the old NB200.  Maybe this dry contact issue is still there too?

 

(CID:134029241)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

In response to DCIM_Support
0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

Hello

Yeah That might be firmware related, but that solution is not an option for this client I'm afraid. They have about 60 NB200 that will be replaced with NB250 units and to buy 60 NB150 pods just to get the dry contacts to work is not an acceptable solution.

 

I have a suspicion it might have something to do with the Sensor identification resistor in the old NBES0304 cable. my cables are about 10 years old and Schneider might have raised the threshold for the identification value in the new firmware so the older cables might just be on the edge of the accepted identification threshold.

But its a really big task to change all the sensor cables if that's the case, I don't have a new NBES0304 cable to measure the values in so I cant confirm my suspicion, but it might explain why the sensor identification connects/disconnects at random intervals, the next values under "dry contact" is not used for the moment in schneiders identification list so a "dry contact" sensor with a lower than specified resistor value is not identified at all and does not show up as a connected sensor.

the easy solution to this problem would be to lower the threshold in the firmware a notch I think, It would be nice to get an official response to this question.

(CID:134032416)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

In response to DCIM_Support
0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2024-04-04 02:44 AM

Another thing i remember was that some old Netbotz units had to small psu's inside so if there were to many sensors on the pod the voltage was going into undervoltage and the pod was nomore aible to see the sensors. 

Maybe someone from Netbotz R&D can bring some light into the dark!

(CID:137730441)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2023-10-22 03:07 AM

0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:53 PM . Last Modified: ‎2023-10-22 03:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore