EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:34 PM . Last Modified: β2024-04-08 12:55 AM
Sometimes when I try to add a CAD file to set the room background, I find some problems. The most usual is "Drawind contains unsupported elements: 1) Wipeout"
I'd like to know the list of all unsupported elements in DCO and how can I ask to the customers the best way to generate a CAD files supported by DCO.
Best regards,
Enric
(CID:116925654)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:34 PM . Last Modified: β2024-04-08 12:55 AM
Hi Enric Climent
New CAD applications keep extending DWG format, so it is easier to list the elements that are supported by the importer. You can find a full list here:
(CID:116925829)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:34 PM . Last Modified: β2024-04-08 12:55 AM
Hi Enric Climent
New CAD applications keep extending DWG format, so it is easier to list the elements that are supported by the importer. You can find a full list here:
(CID:116925829)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:34 PM . Last Modified: β2023-10-22 01:45 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.