Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84755members
354187posts

DCO nfs mount fail

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
orlandogarcia
Ensign Ensign
Ensign
0 Likes
3
799

DCO nfs mount fail

Hi all,

 

The remote backup configuration video is no longer available.

A customer was trying to mount a nfs to DCO and is getting the following error message:

 

Failed to save mount : NFS Error - mount: wrong fs type, bad option, bad superblock on xxxx.com:/ifs/USA/NASHARED/struxureware, missing codepage or helper program, or other error (for several filesystems (e.g. nfs, cifs) you might need a /sbin/mount. helper program) In some cases useful info is found in syslog - try dmesg | tail or so.

 

Looking at older posts seems like the problem is NFS utility is missing?

 

 

 

 

Tags (1)

Accepted Solutions
Jef
Captain Captain
Captain
0 Likes
2
789

Re: DCO nfs mount fail

Hi Orlando,

 

You are right, it seems nfs utility is needed.

SSH log in to server and then run the following command to install the utils (requires Internet access):
sudo yum -y install nfs-utils

 

Kind regards,

Jef

See Answer In Context

Tags (1)
3 Replies 3
Jef
Captain Captain
Captain
0 Likes
2
790

Re: DCO nfs mount fail

Hi Orlando,

 

You are right, it seems nfs utility is needed.

SSH log in to server and then run the following command to install the utils (requires Internet access):
sudo yum -y install nfs-utils

 

Kind regards,

Jef

Tags (1)
orlandogarcia
Ensign Ensign
Ensign
0 Likes
1
769

Re: DCO nfs mount fail

Thank you Jef.

Tags (1)
Jef
Captain Captain
Captain
0 Likes
0
758

Re: DCO nfs mount fail

You are welcome, Orlando,
Kind regards,

Jef

Tags (1)