DCO desktop client forces itself restarted every time while trying to open certain comm rooms. Two problematic comm rooms have been discovered so far.
THIS IS A PRODUCTION ISSUE!
(CID:153092376)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-06 12:22 AM . Last Modified: β2024-04-02 11:35 PM
Hi Yilai,
Can you please provide the following (via your shared site):
copy of the backup file (from the production setup)
name of the problem rooms/locations
client application.log file (usually located in C:\Users\
Thanks,
Kind regards
(CID:153092506)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-06 12:22 AM . Last Modified: β2024-04-02 11:35 PM
Hi Yilai,
Many thanks for providing the data. I have located the issue, caused by child-parent connection issue (in database) between the problem item and its parent storage room. Deleting the problem device will resolve the room opening & client restart issue.
I have sent you a direct email moment ago with details about the problem device and how to fix it.
Kind regards
(CID:153092834)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-06 12:22 AM . Last Modified: β2023-10-22 01:44 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.