DCE TCP Modbus output with two network interfaces

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
jzurera
Lieutenant
Lieutenant
0 Likes
1
250

DCE TCP Modbus output with two network interfaces

Hi,

 

we have a DCE 7.9 with Modbus Output licence and we have a doubt, this DCE has two network interfaces, a public lan and a private lan with all the monitored devices. 

 

Is the output modbus available in both network interfaces?

 

Thanks in advance

Tags (1)

Accepted Solutions
Shaun
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
246

Re: DCE TCP Modbus output with two network interfaces

Hi @jzurera,

 

The modbus output does listen on all interfaces when enabled.  It doesn't listen unless licensed. 

See Answer In Context

Tags (1)
1 Reply 1
Shaun
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
247

Re: DCE TCP Modbus output with two network interfaces

Hi @jzurera,

 

The modbus output does listen on all interfaces when enabled.  It doesn't listen unless licensed. 

Tags (1)