DCE & DCO Linux client installation procedure

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE & DCO Linux client installation procedure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:22 PM . Last Modified: ‎2024-04-08 12:59 AM

0 Likes
5
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:22 PM . Last Modified: ‎2024-04-08 12:59 AM

DCE & DCO Linux client installation procedure

Hi team, 

One of our Clint having red hat Linux for client installation. They have downloaded the linux client from DCE & DCO web client.

How to install the thick clients. Please provide the DCE & DCO thick client installation procedure.

Thanks & Regards

K.Venkat

 

 

(CID:116922651)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:22 PM . Last Modified: ‎2024-04-08 12:59 AM

0 Likes
3
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:22 PM . Last Modified: ‎2024-04-08 12:59 AM

Hi Venkatasubramaniam Krishnamurthy, hi team,

Concerning the installation of DCO-clients on Linux PC, I have the following remarks:

  • the current DCO-clients are only for Linux x86_64;
  • DCO-cliens do not require any separate installation procedure, you just need to unpack the tarballs into the right folder and all;
  • unfortunately I still have not been able to successfully launch any of the three DCO-clients on CentOS-7.3. The reason is the common error "JVM terminated .Exit code = 127".

For example, errors from launch DCO-client:

 

bashStruxureWare Data Center Operation-8.1.0 errorsJVM terminated. Exit code=127 /home/admin/StruxureWare Data Center Operation-8.1.0/jre/bin/java -Xms256M -Xmx768M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=OPERATIONS -Dosgi.nls.warnings=ignore -DSWT_GTK3=0 -jar /home/admin/StruxureWare Data Center Operation-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar -os linux -ws gtk -arch x86_64 -showsplash -launcher /home/admin/StruxureWare Data Center Operation-8.1.0/StruxureWare Data Center Operation -name StruxureWare Data Center Operation --launcher.library /home/admin/StruxureWare Data Center Operation-8.1.0/plugins/org.eclipse.equinox.launcher.gtk.linux.x86_64_1.1.100.v20110505/eclipse_1407.so -startup /home/admin/StruxureWare Data Center Operation-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar --launcher.overrideVmargs -exitdata 20d0007 -application com.apc.isxo.client.bootstrap.application -clean -vm /home/admin/StruxureWare Data Center Operation-8.1.0/jre/bin/java -vmargs -Xms256M -Xmx768M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=OPERATIONS -Dosgi.nls.warnings=ignore -DSWT_GTK3=0 -jar /home/admin/StruxureWare Data Center Operation-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar

And errors from launch DCO Insight-client:

bashStruxureWare Data Center Operation Insight-8.1.0 errorsJVM terminated. Exit code=127 /home/admin/StruxureWare Data Center Operation Insight-8.1.0/jre/bin/java -Xms256M -Xmx1024M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=REPORT_DESIGNER -DSWT_GTK3=0 -Dorg.eclipse.swt.browser.DefaultType=ie -Dorg.eclipse.swt.browser.IEVersion=9999 -jar /home/admin/StruxureWare Data Center Operation Insight-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar -os linux -ws gtk -arch x86_64 -showsplash -launcher /home/admin/StruxureWare Data Center Operation Insight-8.1.0/StruxureWare Data Center Operation Insight -name StruxureWare Data Center Operation Insight --launcher.library /home/admin/StruxureWare Data Center Operation Insight-8.1.0/plugins/org.eclipse.equinox.launcher.gtk.linux.x86_64_1.1.100.v20110505/eclipse_1407.so -startup /home/admin/StruxureWare Data Center Operation Insight-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar --launcher.overrideVmargs -exitdata 2110007 -application com.apc.isxo.client.bootstrap.application -clean -vm /home/admin/StruxureWare Data Center Operation Insight-8.1.0/jre/bin/java -vmargs -Xms256M -Xmx1024M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=REPORT_DESIGNER -DSWT_GTK3=0 -Dorg.eclipse.swt.browser.DefaultType=ie -Dorg.eclipse.swt.browser.IEVersion=9999 -jar /home/admin/StruxureWare Data Center Operation Insight-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar

And errors from launch DCO Lab-client:

bashStruxureWare Data Center Operation Lab-8.1.0 errorsJVM terminated. Exit code=127 /home/admin/StruxureWare Data Center Operation Lab-8.1.0/jre/bin/java -Xms256M -Xmx768M -Xss4M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=DATA_CENTER_LAB -Dosgi.nls.warnings=ignore -DSWT_GTK3=0 -jar /home/admin/StruxureWare Data Center Operation Lab-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar -os linux -ws gtk -arch x86_64 -showsplash -launcher /home/admin/StruxureWare Data Center Operation Lab-8.1.0/StruxureWare Data Center Operation Lab -name StruxureWare Data Center Operation Lab --launcher.library /home/admin/StruxureWare Data Center Operation Lab-8.1.0/plugins/org.eclipse.equinox.launcher.gtk.linux.x86_64_1.1.100.v20110505/eclipse_1407.so -startup /home/admin/StruxureWare Data Center Operation Lab-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar --launcher.overrideVmargs -exitdata 2130007 -application com.apc.isxo.client.bootstrap.application -clean -vm /home/admin/StruxureWare Data Center Operation Lab-8.1.0/jre/bin/java -vmargs -Xms256M -Xmx768M -Xss4M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=DATA_CENTER_LAB -Dosgi.nls.warnings=ignore -DSWT_GTK3=0 -jar /home/admin/StruxureWare Data Center Operation Lab-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar

Someone from the expert has useful tips for solving the above problems?

Very thanks for the support.

 

(CID:116923346)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:22 PM . Last Modified: ‎2024-04-08 12:59 AM

0 Likes
3
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:22 PM . Last Modified: ‎2024-04-08 12:59 AM

Hi Venkatasubramaniam Krishnamurthy, hi team,

Concerning the installation of DCO-clients on Linux PC, I have the following remarks:

  • the current DCO-clients are only for Linux x86_64;
  • DCO-cliens do not require any separate installation procedure, you just need to unpack the tarballs into the right folder and all;
  • unfortunately I still have not been able to successfully launch any of the three DCO-clients on CentOS-7.3. The reason is the common error "JVM terminated .Exit code = 127".

For example, errors from launch DCO-client:

 

bashStruxureWare Data Center Operation-8.1.0 errorsJVM terminated. Exit code=127 /home/admin/StruxureWare Data Center Operation-8.1.0/jre/bin/java -Xms256M -Xmx768M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=OPERATIONS -Dosgi.nls.warnings=ignore -DSWT_GTK3=0 -jar /home/admin/StruxureWare Data Center Operation-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar -os linux -ws gtk -arch x86_64 -showsplash -launcher /home/admin/StruxureWare Data Center Operation-8.1.0/StruxureWare Data Center Operation -name StruxureWare Data Center Operation --launcher.library /home/admin/StruxureWare Data Center Operation-8.1.0/plugins/org.eclipse.equinox.launcher.gtk.linux.x86_64_1.1.100.v20110505/eclipse_1407.so -startup /home/admin/StruxureWare Data Center Operation-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar --launcher.overrideVmargs -exitdata 20d0007 -application com.apc.isxo.client.bootstrap.application -clean -vm /home/admin/StruxureWare Data Center Operation-8.1.0/jre/bin/java -vmargs -Xms256M -Xmx768M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=OPERATIONS -Dosgi.nls.warnings=ignore -DSWT_GTK3=0 -jar /home/admin/StruxureWare Data Center Operation-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar

And errors from launch DCO Insight-client:

bashStruxureWare Data Center Operation Insight-8.1.0 errorsJVM terminated. Exit code=127 /home/admin/StruxureWare Data Center Operation Insight-8.1.0/jre/bin/java -Xms256M -Xmx1024M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=REPORT_DESIGNER -DSWT_GTK3=0 -Dorg.eclipse.swt.browser.DefaultType=ie -Dorg.eclipse.swt.browser.IEVersion=9999 -jar /home/admin/StruxureWare Data Center Operation Insight-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar -os linux -ws gtk -arch x86_64 -showsplash -launcher /home/admin/StruxureWare Data Center Operation Insight-8.1.0/StruxureWare Data Center Operation Insight -name StruxureWare Data Center Operation Insight --launcher.library /home/admin/StruxureWare Data Center Operation Insight-8.1.0/plugins/org.eclipse.equinox.launcher.gtk.linux.x86_64_1.1.100.v20110505/eclipse_1407.so -startup /home/admin/StruxureWare Data Center Operation Insight-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar --launcher.overrideVmargs -exitdata 2110007 -application com.apc.isxo.client.bootstrap.application -clean -vm /home/admin/StruxureWare Data Center Operation Insight-8.1.0/jre/bin/java -vmargs -Xms256M -Xmx1024M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=REPORT_DESIGNER -DSWT_GTK3=0 -Dorg.eclipse.swt.browser.DefaultType=ie -Dorg.eclipse.swt.browser.IEVersion=9999 -jar /home/admin/StruxureWare Data Center Operation Insight-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar

And errors from launch DCO Lab-client:

bashStruxureWare Data Center Operation Lab-8.1.0 errorsJVM terminated. Exit code=127 /home/admin/StruxureWare Data Center Operation Lab-8.1.0/jre/bin/java -Xms256M -Xmx768M -Xss4M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=DATA_CENTER_LAB -Dosgi.nls.warnings=ignore -DSWT_GTK3=0 -jar /home/admin/StruxureWare Data Center Operation Lab-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar -os linux -ws gtk -arch x86_64 -showsplash -launcher /home/admin/StruxureWare Data Center Operation Lab-8.1.0/StruxureWare Data Center Operation Lab -name StruxureWare Data Center Operation Lab --launcher.library /home/admin/StruxureWare Data Center Operation Lab-8.1.0/plugins/org.eclipse.equinox.launcher.gtk.linux.x86_64_1.1.100.v20110505/eclipse_1407.so -startup /home/admin/StruxureWare Data Center Operation Lab-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar --launcher.overrideVmargs -exitdata 2130007 -application com.apc.isxo.client.bootstrap.application -clean -vm /home/admin/StruxureWare Data Center Operation Lab-8.1.0/jre/bin/java -vmargs -Xms256M -Xmx768M -Xss4M -XX:+UseConcMarkSweepGC -XX:+CMSIncrementalMode -XX:+CMSIncrementalPacing -XX:+HeapDumpOnOutOfMemoryError -Dfile.encoding=utf-8 -DbuildType=release -Dosgi.bundlefile.limit=0 -DsyncProduct=DATA_CENTER_LAB -Dosgi.nls.warnings=ignore -DSWT_GTK3=0 -jar /home/admin/StruxureWare Data Center Operation Lab-8.1.0/plugins/org.eclipse.equinox.launcher_1.2.0.v20110502.jar

Someone from the expert has useful tips for solving the above problems?

Very thanks for the support.

 

(CID:116923346)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:23 PM . Last Modified: ‎2024-04-08 12:59 AM

In response to DCIM_Support
0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:23 PM . Last Modified: ‎2024-04-08 12:59 AM

Hi Venkatasubramaniam Krishnamurthy,

Practical recommendations for installing the DCE-client on modern Linux, I wrote on the link 

And about the installation of the DCO-client under Linux, I found only , and it's true for DCE-7.5 unfortunately. I think, that soon I will be able to write practical recommendations for installing the DCO-client on modern Linux for the current version of DCO-8.1.

With best regards.

(CID:116923748)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:23 PM . Last Modified: ‎2024-04-08 12:59 AM

In response to DCIM_Support
0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:23 PM . Last Modified: ‎2024-04-08 12:59 AM

  • unfortunately I still have not been able to successfully launch any of the three DCO-clients on CentOS-7.3. The reason is the common error "JVM terminated .Exit code = 127".

SOLVED: The reason is above the indicated error -- incorrectly downloaded three tarballs (directly from the DCO iso-image). I.e., in these tarballs in the subdirectory jre/bin/java there was only one executable java file. Therefore, after correctly downloading the above three tarballs from a functioning DCO-server, the problem was successfully solved. I.e., in the jre/bin/java subdirectories there was already full JVM installation and all three DCO-clients successfully launched on CentOS-7.

With best regards.

(CID:116923852)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:23 PM . Last Modified: ‎2024-04-08 12:59 AM

In response to DCIM_Support
0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:23 PM . Last Modified: ‎2024-04-08 12:59 AM

Thanks for your great support.

(CID:116923959)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:23 PM . Last Modified: ‎2023-10-22 01:15 AM

0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:23 PM . Last Modified: ‎2023-10-22 01:15 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore