DCE 7.2.4 VM - can only change network settings via VM console.

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE 7.2.4 VM - can only change network settings via VM console.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

0 Likes
8
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

DCE 7.2.4 VM - can only change network settings via VM console.

DCE VM will not accept network setting changes via desktop client. Is this intended?

(CID:93192606)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

0 Likes
2
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

Hi Christopher,

 

Can you advise what network settings you wish to change? The public IP network settings or the network settings on the private network adapter? Is it just the IP address of DCE or all the networks settings? 

You should be able to change network settings on the DCE client, although you will get a warning message about updating the Netbotz appliance post settings as the IP address you configured initially on the DCE is used to send alarm data to the DCE server using that IP address.  

 

Regards,

Breda

 

(CID:93192615)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

In response to DCIM_Support
0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

Hi Breda, specifically its the DNS fields under the Public Lan. I can modify the field and get the warning that the client may restart and the the server may reboot but after accepting that it the client doesnt stop and the server doesnt reboot. If I navigate to another tab and go back to network settings the fields have reverted to the settings configured via the vm console. All other tabs work correctly and the server accepts the change. Its only with network settings that I have to change via the VM console.

(CID:93192648)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

In response to DCIM_Support
0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

I have also tried a manual reboot via the file menu after making the change to see if that will stick the config. It won't.

(CID:93192649)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

Hi Christopher,

 

Thanks for the clarification. When it comes to changing the DNS settings via the DCE client, there is a bug logged on this. It is specific to the DCE VM. On the hardware version the issue is not present when changing the DNS settings. 

 

For the moment the DNS settings for versions 7.2.1 and higher needs to be changing on the VM console. The username/password to this VM console is apcsetup/apcsetup. 

 

Regards,

B

 

(CID:93192713)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:15 AM . Last Modified: ‎2024-04-10 01:17 AM

This has been fixed in DCE 7.2.6 which has just been completed and will be announced shortly.

(CID:93194025)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:16 AM . Last Modified: ‎2024-04-10 01:16 AM

0 Likes
1
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:16 AM . Last Modified: ‎2024-04-10 01:16 AM

I was also having this problem and was able to change the DNS setting via the console but there is no option to change the Hostname or Domain from the console. Is there a manual way to change the Hostname or Domain, if not, do we have a rough release date for DCE 7.2.6?
I can change the Hostname from the client, but the Domain is still an issue.

(CID:93194078)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:16 AM . Last Modified: ‎2024-04-10 01:16 AM

In response to DCIM_Support
0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:16 AM . Last Modified: ‎2024-04-10 01:16 AM

Hi Justen, You can contact support today and get 7.2.6. We're still working on officially launching it, but it is technically available now. -Scott

(CID:93913091)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:16 AM . Last Modified: ‎2023-10-31 10:24 PM

0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:16 AM . Last Modified: ‎2023-10-31 10:24 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of