We have installed 6 Emerson Liebert PCW PH170 like this to meet our cooling requirements in our data center room:
They come equipped with a downflow module, I haven't found any gnome in DCO so I have used the NetworkAIR FM DX Air Cooled 208-230v / 60Hz, Downflow gnome to model it.
The problem I'm facing is that these units are placed in separate rooms from the server room, the push the cold air below the raised floor of the server room and it is distributed through perforated tiles that are in the cold aisles. The hot air is then again captured by rows of perforated tiles placed in the dropped ceiling.
(In this image, IT 1-1, 1-2, etc, are the cooling units. The cool air is distributed through the middle of each of the three rack modules in blue, while the hot air is collected in the red bar of tiles).
(detail of the cooling units)
(detail of the hot aisle tiles in the dropped ceiling)
In the design I have made in DCO, I can't get no cooling measures from the server room because of the absence of the cooling units:
Only when I put cooling units the same room, things start to change, but it's not valid because the equipment is in the adjacent rooms:
Is there any workaround or fix to sort it out? Or there is any other gnome that can do this? I have also tried to place vertical grilles in the walls and simulate the air flow from the emerson cooling units but the results are not the same.
(CID:93193452)
Hi Manuel,
What an absolutely amazing description of your setup and issue! wow
The exact problem you are describing is possible from v7.4 of DCO.
The documentation can be found here: Designs with CRAC Units Placed Outside the Room
Hopefully this is enough for you to get this modelled and working in your setup? Otherwise I trust you will let us know.
(CID:93193463)
Hi Manuel,
(CID:93193463)
Posted: 2020-07-02 09:34 AM . Last Modified: 2024-04-10 01:10 AM
Soren,
I have a similar situation with CRAC units outside the hall but the difference being there is no drop ceiling and the return air grills are located on the wall. Is there a way to model that?
(CID:93193467)
Hi James,
There is a way to model your setup as well assuming you have v7.4.
You need to use the "Vertical Grille" genome from the genome library.
Those can then be added to the wall of the room where located and size adjusted in the "Physical" properties section of the vertical grille it self.
In the "Cooling" property page of the vertical grille you specify what the airflow through the grille will be. Also the temperature can be specified if needed. Otherwise the room default is used which can be found in the "Cooling" properties of the room (Cooler Supply).
You must add at least 2 vertical grilles to the room 1 with air going into the room and 1 with air going out of the room.
The vertical grilles is not depended on the CRAC units. That means they will assume "infinite" cooling capabilities being able to deliver what is specified in airflow and temperature.
Example, bottom grille at the left provides air, right side grill takes air out of the room
(CID:93193552)
Soren,
Would I have to remove the CRACR units?
At the moment I have the CRAC units outside of the room with perforated floor tiles in the DC (as per actual setup). Which supplies air correctly but the problem is with the return air as there are wall grilles that the return air passes through which I cant model as you need two vertical grilles on DCO. Is there any way to model the return air correctly (without adding a drop ceiling or another work around)?
(CID:93193569)
Hi James,
You do not need to remove the CRACs they can coexist with the vertical grilles.
At present there are no way to model your exact setup. As you also state you need 2 vertical grilles providing air in and out of the room. Depending on the location of the return air grill in your room it might make sense to do a work around with drop ceiling and ceiling tiles which is the only work around at present. Besides of course not modelling the return air which I guess would be a worst case scenario in your setup.
I will track your setup in our feature request database as a setup that is currently not supported.
(CID:93193592)
Soren, To bring this issue up again. If I have a CRAC unit outside the room which say has airflow set to 100 m3/h and I have a vertical grille in front supplying air into the room and that is set to 100 m3/h, will the model assume there is 200 m3/h of air being supplied?
(CID:94601639)
Hi James, The system will understand this as 200m3/h supplied into the room. In order to make the vertical grille functionality work you need to "disable" the CRAC units by setting them to not supplying air (setting air flow to 0m3/h)
(CID:94601651)
Thanks Soren,
Would it be fair to say that DCO can't handle CRAC units being outside the room without having to do a number of workarounds? How would I go about getting this raised with the programmers at Schneider, unless that it yourself, as I currently cannot represent all, bar one, of our DCs cooling requirements?
(CID:94601680)
Hi James, It depends on how the "CRAC outside of the room" setup is in my opinion. It would be fair to say that having CRAC units outside the room and air out of the room via grille(s) is not well supported. I will track CRAC units placed outside the room and return air out of the room via grille(s) in our feature request database. The feature request system is the interface towards our engineering/programmers/development team. Are there any other setups then the one explained that you are not capable of modelling?
(CID:94601947)
Søren Bruncke Mikkelsen,
The two setups I have are that can't be modelled correctly
Do those two scenarios make sense? If not I can provide more information.
James
(CID:94601962)
Posted: 2020-07-02 09:35 AM . Last Modified: 2024-04-10 01:10 AM
Hi James, Sorry I did not answer your question I just tracked this right away since they make absolute sense. If more information is needed we will get in contact with you.
(CID:94602604)