Hi,
I am facing a problem with cooling in DCO 7.5, as shown in picture my actual design is on the right side of picture everything is configure properly, but when I press the cooling tab the one side of racks goes red. you can also see the error in 3rd picture. ''The System cannot compute: cold Aisle: Hot air is blowing into the clod aisle.''
If I put one extra cabinet in the front of the red row then cooling are working normal. I just want to know where is the problem in my actual design.
(CID:105457827)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:37 PM . Last Modified: 2024-04-09 01:54 AM
Hi Ali,
It might be basically something to do with modelling your cold aisle containment system (such as its 'size', if it is slightly small and not being able to include all assets as it should ). I will send you an invite to my =S= box shortly, just in case if you would kindly share a copy of the solution with me, then I can take a look, thanks.
Kind regards
(CID:105457944)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:37 PM . Last Modified: 2024-04-09 01:54 AM
Hi. It looks to me like you have your racks oriented with the backs to each other. The front of the racks on the green row are at the top of the drawing and the front of the racks on the red row are on the bottom of the drawing. Rotate all the racks so the edge with the heavier line is facing the other row. The way you have them drawn looks like the hot aisle is between the two rows. The hot air from both rows are blowing into the cold aisle.
(CID:105459908)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:37 PM . Last Modified: 2024-04-09 01:53 AM
Sorry, i have the same problem and i didn't understand the solution you guys gave here.
Can someone help?
(CID:134686841)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:37 PM . Last Modified: 2023-10-31 10:22 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Welcome to your new personalized space.
of