EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-03 04:41 AM . Last Modified: ‎2024-04-08 11:35 PM
Hi all
Ive just entered a load of servers into a rack in DCO.
The racks physical power limit is 24.54kW (
estimated load is 9.55kW
Potential Failover load is 9.32kW
Im at a loss to understand what this error means with these figures ?
thanks
(CID:106891457)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-03 04:41 AM . Last Modified: ‎2024-04-08 11:35 PM
The mentioned recommendation looks a the breaker limit for each power phase on each rack PDU, and will show up if the estimated load + failover load on that particular breaker exceeds the limit.
E.g. if you have a rack with 1 three phase rack PDU and connected all servers to L1, then you have exceed the breaker capacity of L1 at 1/3 of the total rack capacity.
(CID:106891475)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-03 04:41 AM . Last Modified: ‎2023-10-31 10:17 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.