Alerts for Netbotz sensors going offline even if Netbotz is offline

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Alerts for Netbotz sensors going offline even if Netbotz is offline
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

0 Likes
9
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Alerts for Netbotz sensors going offline even if Netbotz is offline

We have our Netbotz connected to various sensors (humidity, leak rope, temperature, etc). One of our Netbotz semi-crashed a few days ago (I could log in via Advanced View but got an HTTP 200 error whenever I tried to do anything, and I couldn't see any sensors attached to the unit in Advanced View) and the only notification we received from Data Center Expert was a critical communication error that the Netbotz was offline.

 

If this happens again we'd like Data Center Expert to send us alerts that the sensors are offline, too, so that it's clear that there's a serious problem going on. The sensors monitor conditions in our data center, which holds a lot of expensive equipment, so it's very important that we know what is happening in the room and respond in a timely manner. Is that possible? As it currently stands, the Netbotz has to be fully functional for us to receive an alert that, for example, the camera pod is offline/unplugged.

(CID:132669858)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

0 Likes
7
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Hi Dominic,

The NetBotz appliance (3xx, 4xx, and 5xx models) alerts for the individual sensors by itself. Should it lose comm with a sensor, it is responsible for alerting. This is different than the SNMP devices DCE monitors.

DCE on the other hand alerts when it loses comm with a NetBotz appliance.  It alerts using a login that has an e-mail associated with it as well as that login having access to the appliance. This is by design. It was designed this way specifically so that you do not receive hundreds of e-mails about a NetBotz appliance and every single one of it's attached sensors.

Please also note that just because the NetBotz loses comm with DCE, that does not necessarily mean the NetBotz appliance itself is off-line or has lost communications with it's sensors. 

Perhaps a special user account in DCE with an e-mail address that will specifically go to someone that knows if NetBotz A goes off-line, Sensors 1, 2, and 3 may also be off-line. 

 

Steve

 

(CID:132669883)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

0 Likes
7
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Hi Dominic,

The NetBotz appliance (3xx, 4xx, and 5xx models) alerts for the individual sensors by itself. Should it lose comm with a sensor, it is responsible for alerting. This is different than the SNMP devices DCE monitors.

DCE on the other hand alerts when it loses comm with a NetBotz appliance.  It alerts using a login that has an e-mail associated with it as well as that login having access to the appliance. This is by design. It was designed this way specifically so that you do not receive hundreds of e-mails about a NetBotz appliance and every single one of it's attached sensors.

Please also note that just because the NetBotz loses comm with DCE, that does not necessarily mean the NetBotz appliance itself is off-line or has lost communications with it's sensors. 

Perhaps a special user account in DCE with an e-mail address that will specifically go to someone that knows if NetBotz A goes off-line, Sensors 1, 2, and 3 may also be off-line. 

 

Steve

 

(CID:132669883)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

In response to DCIM_Support
0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Steve,

Thanks for the prompt reply. Is there any documentation/KB article that states that it is "by design" that DCE only alerts on a communication error with a Netbotz and not with all its sensors?

At the moment the e-mail that DCE sends us states that the communication error is with an IP - is there any way to make it say, for example, the hostname of the Netbotz? Or does DCE just pull the name/IP from the "hostname" column in DCE?

(CID:132669912)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

In response to DCIM_Support
0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Hi Dominic,

 

No, there is no documentation I am aware of stating this specifically and that it is by design however ever since NetBotz communicated with NetBotz Central, (predecessor to ISXC then DCE,) the NetBotz alerting has always been "At the Edge". NetBotz alerted for themselves in case the central server went down, the devices would still alert for themselves...and they still do. If you've ever configured an alarm for a NetBotz 3xx, 4xx, or 5xx device in DCE, you know that unlike an SNMP device, the configuration is being pushed to the device itself and not saved on the DCE server for alerting.

 

Simply by understanding the design of how it works should allow you to understand why it doesn't work the way you're looking for it to work. Maybe something like this would make for a good knowledge base article and I will look into that.

 

Steve

(CID:132669944)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

In response to DCIM_Support
0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Steve,

Thanks again for the prompt reply. I understand that the Netbotz alert for themselves, and we make good use of that facility. We're just trying to see if there's a way to get alerts when the Netbotz itself goes down, other than the single "device offline" alert from DCE.

 

Are you able to answer my question about configuring the "critical communication" alert from DCE? How do I get it to tell me which Netbotz is offline, rather than just an IP?

(CID:132669962)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

In response to DCIM_Support
0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Hi Dominic,

 

Sorry but there is no configuration for these off-line alerts. Sorry if I missed that part.

I did look into it and there is an enhancement request in the system for this part of the issue. I've added your post to the request.

 

Steve

(CID:132669965)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

In response to DCIM_Support
0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Steve,

Do you know if DCE uses the "hostname" for the alert or does it always use the IP regardless of whether or not there is a hostname in the hostname column in DCE for that device?

(CID:132669967)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

In response to DCIM_Support
0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:56 PM . Last Modified: ‎2024-04-04 04:00 AM

Dominic,

I've not tested this nor is it documented. If there's a hostname field in the e-mail, I would expect it to send whatever DCE shows in the hostname column but that's not to say it will definitely send that way. Again, the enhancement request does include the request forsome configuration options.

(CID:132669969)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:57 PM . Last Modified: ‎2024-04-04 04:00 AM

In response to DCIM_Support
0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:57 PM . Last Modified: ‎2024-04-04 04:00 AM

Okay thanks very much!

(CID:132669973)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:57 PM . Last Modified: ‎2023-10-20 05:00 AM

0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:57 PM . Last Modified: ‎2023-10-20 05:00 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore