Dear team,
I am using DCE 7.6.0 and i wanted to get alarm notifications via HTTP Post, Please do let me know what is the procedure to use this feature and inwhich format we can get alarms by using macros.
Regards
MS
(CID:139692734)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 04:54 PM . Last Modified: β2024-04-03 04:20 AM
Hi Muhammad,
To receive an HTTP post, you must have an HTTP receiver running awaiting the post. This receiver must then parse the XML data sent from DCE. If you are not familiar with this process, I strongly recommend using another feature such as sending to an FTP server or Windows share.
Thanks,
Steve
(CID:139692969)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 04:54 PM . Last Modified: β2024-04-03 04:20 AM
Dear Steve,
Can you please guide its procedure.
(CID:139693496)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 04:54 PM . Last Modified: β2024-04-03 04:20 AM
Hi Muhammad,
First, go to "Alarm Configuration" and "Manage Alarm Actions"
Next, either select or create HTTP post:
Next, you name the action, give it a target URL, then a user name and password (and verify password)
That's all there is to creating the action.
After that, you need to either associate that action to a policy or create a new policy to associate with.
If you're in the alarm configuration tab, you can see the notification policies and can create one. You can use the menus too.
Hit that green '+' sign to add policy. Name it and dd the action to the policy
Then simply add devices or thresholds.
All the rest is up to you. You need to create an HTTP page that accepts these posts and accepts and parses the XML data. That's the hard part and that's why I suggest using e-mail or other actions.
Thanks,
Steve
(CID:139693735)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 04:54 PM . Last Modified: β2023-10-20 05:00 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.