Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us enhance search functionality and deliver the results you need faster and more accurately. Click here to take the survey Thank you for helping us build a better Community experience!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-15 01:55 AM . Last Modified: 2022-10-19 12:48 AM
Hi,
base on:
there is no possibility to integrate PCNS with DCE but DDF file for PCNS currently exist.
is this mean PCNS can be add to DCE?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-03 05:09 AM
Hi @PrzemekSz,
It is possible to monitor a PCNS installation from DCE through SNMP polling. It will monitor items such as NMC to UPS comms, ports being used, if a shutdown is in progress, and more.
Some screen captures on device sensors and how it would show in DCE can be found here: https://community.se.com/t5/EcoStruxure-IT-forum/PCNS-4-2-and-SxW-DCE-7-4-3-device-quot-model-quot-i...
PCNS can not be integrated into DCE to be able to shutdown DCE.
Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-03 05:09 AM
Hi @PrzemekSz,
It is possible to monitor a PCNS installation from DCE through SNMP polling. It will monitor items such as NMC to UPS comms, ports being used, if a shutdown is in progress, and more.
Some screen captures on device sensors and how it would show in DCE can be found here: https://community.se.com/t5/EcoStruxure-IT-forum/PCNS-4-2-and-SxW-DCE-7-4-3-device-quot-model-quot-i...
PCNS can not be integrated into DCE to be able to shutdown DCE.
Regards,
Cory