Creating DCE Alerts

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Creating DCE Alerts
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
10
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

Creating DCE Alerts

Hello,

I am new to DCE, and I am a bit confused on how to setup alerts in DCE? At first I thought the the NMC in the device would forward detected alerts to DCE which in turn would send the alert out via configured email addresses and SMTP gateways. That doesn't appear to be the case though. Thus, I was looking for some documentation for setting this up. For example, how would I go about creating an alert that would let me know any time one of my APC UPS'es have a bad battery pack?

Thanks,

Jon

(CID:105466320)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
8
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Jon,

That is correct, the NMC does send its alerts via SNMP to Data Center Expert and then Data Center Expert will push out of the email alerts. Below is a link to documentation on how to configure your email and email alerts.

http://www.schneider-electric.us/en/faqs/index?page=content&id=FA225766

In regards to your question about a bad battery pack alert, each APC UPS should have a Device Alarm in Data Center Expert that signifies that there is a bad battery. You can check this by going into the Alarm Configuration Perspective and go to the Device Alarm Configurations for that UPS.

Below is picture of what it looks like in our Data Center Expert Server:

 

Kind Regards,

Andrew

(CID:105466325)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
8
1963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Jon,

That is correct, the NMC does send its alerts via SNMP to Data Center Expert and then Data Center Expert will push out of the email alerts. Below is a link to documentation on how to configure your email and email alerts.

http://www.schneider-electric.us/en/faqs/index?page=content&id=FA225766

In regards to your question about a bad battery pack alert, each APC UPS should have a Device Alarm in Data Center Expert that signifies that there is a bad battery. You can check this by going into the Alarm Configuration Perspective and go to the Device Alarm Configurations for that UPS.

Below is picture of what it looks like in our Data Center Expert Server:

 

Kind Regards,

Andrew

(CID:105466325)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

In response to DCIM_Support
0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Andrew,

Thanks for the info! One more question. My DCE shows this when I search for Battery:

It shows (17) for "Battery Needs Replacement". Does this mean that the 17 devices listed here have bad battery packs? If so, why didn't DCE alert me to this? Or, does this mean that there are 17 devices that this alarm is applied to?

 

Thanks,

Jon

(CID:105466918)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

In response to DCIM_Support
0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Jon, The alarms in the device alarm configurations shows what alarms the unit is capable of sending to StruxureWare, it does not mean that the unit has a bad battery pack. So you are correct in saying, that there is 17 devices that the "Battery Needs Replacement" alarm applies to. Kind Regards, Andrew

(CID:105466920)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

In response to DCIM_Support
0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

Thanks Andrew,

One last question (I hope). I was playing around with custom thresholds, and I ended up creating one and assigning it to specific device. Now I can't get rid of it. If you look at the screen-shot, I click on "State - Battery Replacement Status" and then I select "Remove Selected Thresholds"; however, nothing happens. How do I get rid of this custom threshold?

Thanks!

Jon

(CID:105466923)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

In response to DCIM_Support
0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Jon, You are unable to remove this alarm because you are in currently in the Notification Policy window, in this window you are just adding/removing thresholds to your Notification Policy. If you want to remove the alert you will need to go Threshold Alarm Configurations of the device, right click on the threshold and choose "Delete Thresholds...". Also see the picture I have attached to this comment for this illustration. Kind Regards, Andrew

(CID:105466925)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

In response to DCIM_Support
0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

So I was able to remove the threshold from the alarm, but I was not able to delete the threshold as "Delete Thresholds..." was not an option.

 

(CID:105466929)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

In response to DCIM_Support
0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Jon, That is correct, you won't be able to delete the "Communication Status" Threshold, you will only be able to disable that Threshold alarm by going to Edit Thresholds and changing the Enabled option from "Yes" to "No". The Communication Status is added by default by StruxureWare Server to notify you if you can no longer communicate with the device. Kind Regards, Andrew

(CID:105466932)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

In response to DCIM_Support
0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:08 AM . Last Modified: ‎2024-04-09 01:00 AM

Thanks Andrew for all your help, I really appreciate it! Can you recommend any documentation on creating custom alerts/notifications? I would like to read more about this aspect of DCE.

(CID:105466933)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 01:00 AM

In response to DCIM_Support
0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Jon, The Online Help guide has a fair amount of information about creating alerts. You can find the Online Help guide in the link below. I was able to find that information in the Online Help Guide on pages 146-167. http://dcimsupport.apc.com/display/public/UADCE725/User+assistance+for+StruxureWare+Data+Center+Expe... Kind Regards, Andrew

(CID:105466931)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2023-10-31 10:22 PM

0 Likes
0
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2023-10-31 10:22 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore