Upgrade Path for DCE 7.2.5 to 7.2.7

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Upgrade Path for DCE 7.2.5 to 7.2.7
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
4
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 01:00 AM

Upgrade Path for DCE 7.2.5 to 7.2.7

We decided to migrate the physical DCE version 7.2.5 to a virtual DCE version 7.2.7. The virtual DCE is up and running, and we have applied the new license key. However, when we tried to restore to 7.2.7 the backup done in 7.2.5, we could not see any of the backup files. Reading the forum, someone mentioned that we can only restore a backup performed in the same DCE version.

Question:

  1. do we have to upgrade the physical DCE from 7.2.5 to 7.2.6 first, or can we upgrade the physical DCE directly from 7.2.5 to 7.2.7?
  2. our 7.2.5 have 1TB disk space, but we only use 300GB currently. furthermore, we intend to only migrate the Configuration without migrating the CCTV footage, does that mean we still need to create a 1TB volume in the virtual DCE? because I read in the migration documentation that the virtual DCE has to match the configuration of the physical DCE (e.g. CPU, RAM, Disk space etc.)

Thanks very much!

Cheers, Simon

(CID:105466338)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 12:59 AM

0 Likes
0
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 12:59 AM

Dear Simon,

Please find my responses to your query.

  1. do we have to upgrade the physical DCE from 7.2.5 to 7.2.6 first, or can we upgrade the physical DCE directly from 7.2.5 to 7.2.7?
    1. Yes, DCE version 7.2.5 has to be upgraded to version 7.2.6 before upgrading it to 7.2.7. You are correct that restore of the DCE backup can be performed in the same DCE version.

  2. our 7.2.5 have 1TB disk space, but we only use 300GB currently. furthermore, we intend to only migrate the Configuration without migrating the CCTV footage, does that mean we still need to create a 1TB volume in the virtual DCE? because I read in the migration documentation that the virtual DCE has to match the configuration of the physical DCE (e.g. CPU, RAM, Disk space etc.)
    1. In my opinion, Storage space of the virtual appliance can be increased by the user based on the requirement. It does not require 1 TB disk space need to be allocated during the installation itself. It is correct that VM specs has to match with the configuration of the Physical DCE. From the Manual: 

      Deploy the demo version OVA, and configure it using the hardware equivalents for
      the StruxureWare Data Center Expert Basic, Standard, or Enterprise server from
      which you are migrating. The available disk space for the virtual appliance must
      be greater than the disk space used by the hardware server.

      Hard disk settings: To increase storage for the virtual appliance, you can create additional
      hard disks. You cannot change the size of an existing hard disk, or remove a hard disk once
      it has been created. An error will occur on the primary interface, and the StruxureWare
      Data Center Expert virtual appliance will not start.
      Changes in the disk space will take effect once the StruxureWare Data Center Expert virtual
      appliance has restarted.
      The "Storage Settings" display, accessed from the Server Administration Settings option
      in the System menu, shows the total storage space available for the virtual appliance, not
      the individual hard disks.
      Note: To store large amounts of surveillance data, using a remote repository is
      recommended.

    2. Adding disk space to a virtual appliance
      To increase storage for the virtual appliance, you must create additional hard disks.
      You cannot change the size of an existing hard disk, or remove a hard disk once it has been
      created. An error will occur on the primary interface, and the StruxureWare Data Center
      Expert virtual appliance will not start.
      1. Gracefully shut down the virtual appliance.
      2. In your virtual server console, select the option to add a hard disk.
      3. Choose the hard disk size.
      See StruxureWare Data Center Expert virtual server equivalent configurations.
      4. Choose thin or thick provisioning.
      5. Power on the virtual appliance. StruxureWare Data Center Expert Changes in the disk space will take effect once the StruxureWare Data Center Expert virtual appliance has restarted. 

      Do not shut down the virtual appliance while the disk reconfiguration process is running.
      The "Storage Settings" display, accessed from the Server Administration Settings option
      in the System menu, shows the total storage space available for the virtual appliance, not
      the individual hard disks.


      Note: To store large amounts of surveillance data, using a remote repository is
      recommended.

    I hope this helps. 

    Regards,
    Bala

(CID:105466345)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 12:59 AM

0 Likes
0
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 12:59 AM

Simon,

You will need to upgrade your physical appliance to DCE 7.2.7 first.  Your local technical support shouldbe able to assist with the necessary upgrade links.  A backup can then be created and brought into you virtual DCE appliance.  The disk space just has to be greater than the amount being used by your physical DCE server.

"The available disk space for the virtual appliance must
be greater than the disk space used by the hardware server."

Best Regards,

Cory

(CID:105466343)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 12:59 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 12:59 AM

Dear Simon,

Please find my responses to your query.

  1. do we have to upgrade the physical DCE from 7.2.5 to 7.2.6 first, or can we upgrade the physical DCE directly from 7.2.5 to 7.2.7?
    1. Yes, DCE version 7.2.5 has to be upgraded to version 7.2.6 before upgrading it to 7.2.7. You are correct that restore of the DCE backup can be performed in the same DCE version.

  2. our 7.2.5 have 1TB disk space, but we only use 300GB currently. furthermore, we intend to only migrate the Configuration without migrating the CCTV footage, does that mean we still need to create a 1TB volume in the virtual DCE? because I read in the migration documentation that the virtual DCE has to match the configuration of the physical DCE (e.g. CPU, RAM, Disk space etc.)
    1. In my opinion, Storage space of the virtual appliance can be increased by the user based on the requirement. It does not require 1 TB disk space need to be allocated during the installation itself. It is correct that VM specs has to match with the configuration of the Physical DCE. From the Manual: 

      Deploy the demo version OVA, and configure it using the hardware equivalents for
      the StruxureWare Data Center Expert Basic, Standard, or Enterprise server from
      which you are migrating. The available disk space for the virtual appliance must
      be greater than the disk space used by the hardware server.

      Hard disk settings: To increase storage for the virtual appliance, you can create additional
      hard disks. You cannot change the size of an existing hard disk, or remove a hard disk once
      it has been created. An error will occur on the primary interface, and the StruxureWare
      Data Center Expert virtual appliance will not start.
      Changes in the disk space will take effect once the StruxureWare Data Center Expert virtual
      appliance has restarted.
      The "Storage Settings" display, accessed from the Server Administration Settings option
      in the System menu, shows the total storage space available for the virtual appliance, not
      the individual hard disks.
      Note: To store large amounts of surveillance data, using a remote repository is
      recommended.

    2. Adding disk space to a virtual appliance
      To increase storage for the virtual appliance, you must create additional hard disks.
      You cannot change the size of an existing hard disk, or remove a hard disk once it has been
      created. An error will occur on the primary interface, and the StruxureWare Data Center
      Expert virtual appliance will not start.
      1. Gracefully shut down the virtual appliance.
      2. In your virtual server console, select the option to add a hard disk.
      3. Choose the hard disk size.
      See StruxureWare Data Center Expert virtual server equivalent configurations.
      4. Choose thin or thick provisioning.
      5. Power on the virtual appliance. StruxureWare Data Center Expert Changes in the disk space will take effect once the StruxureWare Data Center Expert virtual appliance has restarted. 

      Do not shut down the virtual appliance while the disk reconfiguration process is running.
      The "Storage Settings" display, accessed from the Server Administration Settings option
      in the System menu, shows the total storage space available for the virtual appliance, not
      the individual hard disks.


      Note: To store large amounts of surveillance data, using a remote repository is
      recommended.

    I hope this helps. 

    Regards,
    Bala

(CID:105466345)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 12:59 AM

0 Likes
0
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2024-04-09 12:59 AM

Hi Bala and Cory,

Thanks so much for the fast and useful response! I know what to do now. Thanks!

Cheers, Simon

(CID:105466402)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2023-10-31 11:40 PM

0 Likes
0
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:09 AM . Last Modified: ‎2023-10-31 11:40 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore