BCPM Sensor Value "Unplugged" in DCE 7.3.1

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • BCPM Sensor Value "Unplugged" in DCE 7.3.1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
7
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

BCPM Sensor Value "Unplugged" in DCE 7.3.1

Hi all

All ModBus BCMP devices are online in the DCE 7.3.1 but the sensor values is shown as "unplugged".

What can be done in this case? 
 

(CID:105466295)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
0
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

Dear Faruk, I would verify if the BCMP responds to Modbus Over TCP register IDs as per the DDF file request Register IDs by using any freeware Modbus scan software. Were these sensor values responding with values before? or Is the BCPM added newly to DCE 7.3.1? Is this issue there from the time of integration with DCE? If not, when this issue has started? Could you please confirm if there is an Ethernet gateway between DCE and BCPM? Does BCPM register IDs poll and respond to the poll when you can scan the BCPM values before gateway via Modbus RS485?

(CID:105466307)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
0
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Faruk, did you see this comment from Balaraman? Best, Stine

(CID:105466890)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
0
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

Hello Balaraman

Thanks a lot for your reply. All the connections to the Modbus devices are fine. 

The issue with the sensor values shown as "unplugged" was after I have upgraded to the latest DCE version 7.3.1. 
After the roll back to the prior version those issues have dissapeard.

I have also faced issues with the NSX, Masterpact, BCPM devices sending communication error from dce, but the network connection is available at all the times, between all this devices I have a egx100.

I assume there is maybe an issue with the DDF's?

(CID:105469907)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
0
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

Dear Faruk, I do not think there may be an issue with DDF as the sensors values are not unplugged errors with the previous DCE version(I assume version 7.2.7). After upgrading to DCE to version 7.3.1, Its good idea to verify if the respective Modbus Over TCP DDF file is added to version 7.3.1 if the Modbus over TCP sensors values are showing unplugged. You can also if the sensors values start showing after the DCE modbus device polling as per Global Scan Settings. Global Scan Settings can be checked under Device--Modbus Device Communication Settings. While the DCE shows unplugged for the sensor value, please use the modscan software to see if the value responds to the polling via Modbus over TCP polling. Note: I would suggest you to take the Full Backup of DCE before upgrading the DCE version.

(CID:105467292)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
0
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

Hi Sirs, 

I can report that after the migration from 7.2.7 to 7.3.1 all the Modbus Devices are in status "unplugged" 

Only the snmp devices work and show values. Normaly a simple upgrade of client version don't have to be an issue for us!

hope you will find a solution , for me the solution for the moment is to restore the back up of the server..

(CID:105469627)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

0 Likes
0
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2024-04-09 01:00 AM

Dear Balaraman
I have verified the DDF and there were in, I have also tried to remove one and re-add again also adding a new device does not work, it just shows the status "intializing".

Any changes under polling settings does not help, I have realized that under the column "last seen online" it says "never".

 

(CID:105469635)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2023-10-31 10:17 PM

0 Likes
0
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:07 AM . Last Modified: ‎2023-10-31 10:17 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore