Real World Mapping Usage and References

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Real World Mapping Usage and References
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
318
AndrewScott
Admiral AndrewScott
109
BevanWeiss
Spock BevanWeiss
96
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Simon_Lee
Simon_Lee Cadet
Cadet

Posted: ‎2020-02-05 07:36 AM . Last Modified: ‎2023-05-03 12:17 AM

0 Likes
7
3519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-05 07:36 AM . Last Modified: ‎2023-05-03 12:17 AM

Real World Mapping Usage and References

The Geo Location and Mapping features have been available in Geo SCADA for a few years now. Is anyone using these features in the "real world"?

 

We have UK Geo SCADA customers who have been using the product for many years and are now looking to exploit these features in their latest upgrades. I would like to be able to provide them with some real world references, and perhaps facilitate a call with other Geo SCADA customers/users to discuss some of their use cases and benefits they have received from using the Geo Location features.

Labels
  • Labels:
  • SCADA
  • Telemetry
  • ViewX
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
geoffpatton
Captain geoffpatton
Captain

Posted: ‎2020-02-05 11:36 AM

0 Likes
1
3514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-05 11:36 AM

I have not used this feature in the real world yet, but I thought this might be helpful to you as there are Pros and Cons to any change. If your customers have Maps on Mimics these might be a Cons for them also. The Cons may not be a big deal, but addressing them from the beginning is usually best. These are the Cons that we found when checking what would be different for the one customer I have considering using it.

 

They will lose some things that they currently have using a Mimic with PNGs of map area on it.

 

They have at least 5 different station types and there are only 3 different icon shapes for the Geo Map, also controlling which Icon you get is not as simple as I think it could be, which may make adding new sites more difficult for their administrators. Their current station label's background color is used to indicate the station type.

 

The Geo map icons only use the Alarm state colors for site status. Their current Map symbol has a lot more colors based on alarms, some specific statuses, and the communication state. They have a Legend for these colors too.

 

The Geo map icons do not have a label only a tooltip if you point at them. On their current mimic map, they have the station number on a label to the right of their station status icon.

 

They sometimes put other Labels and values on a map Mimic and you cannot have anything but the Icons on the Geo Maps.

 

Navigation to the site requires a right-click in the icon and then selecting the Default View, or Alarm View. Not a big deal but it is nicer to just left-click and goto the site.

 

The biggest concern is that it will be more difficult to assess station statuses at a glance and easily find stations on the Geo Map.

 

Also, the biggest Cons to sticking with PNGs on Mimics are having to update the PNGs when something changes on a map, and the zoom-ability is less robust.

Reply

Link copied. Please paste this link to share this article on your social media post.

Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2020-02-05 12:56 PM . Last Modified: ‎2022-10-19 02:33 AM

In response to geoffpatton
0 Likes
0
3508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-05 12:56 PM . Last Modified: ‎2022-10-19 02:33 AM

Two other posts to the forums about the integration of Geo/GIS data into Geo SCADA:

 

https://community.se.com/t5/Geo-SCADA-Expert-Forum/Offline-Map-Geo-SCADA-ClearSCADA/td-p/184590

 

https://community.se.com/t5/Geo-SCADA-Expert-Forum/Imported-GIS-Exportable-file-formats-supported-by...

 

The second link is to my question of how to get the Geo/GIS data into Geo SCADA if you are limited by your IT department on what network connections to the Internet you have. When I asked the question, the answer I got was not that it is impossible, but it maybe frowned upon by my IT department, and some other options were provided.

 

It wasn't until later that I found out that the Geo Maps won't allow you to overlay points, mimics, or symbols of your own. That limitation goes against what I was hoping to accomplish.

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-05 01:33 PM

0 Likes
0
3504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-05 01:33 PM

There's not much to lose in utilising the GeoLocation aspect.  You just need to assign a Location to each element that it makes sense to.  This would normally be at the site level, and in mature ClearSCADA systems was already being done using Parameters anyway, so it provided this capability more natively, whilst allowing some enhancements to it (such as the ability to query easily on location etc).

 

The current mapping interface is a bit limited in my opinion.  But it's only been present for a few years, and features do tend to move quite slowly in the SCADA world.  As others have noted, there is a restriction on the use of 'map symbols', so there are only a small number of very generic shapes built in, with currently no way to use custom shapes.  This was one of the things that was going to be enhanced shortly after release of the mapping component, but it appears the priority of this has dropped.

 

Display of information on the maps is also a bit limited.

You can have a site represented as one of the limited symbols, and you can pick the foreground colour for it, and whether it blinks (flashes) or not.

It will just show up as the symbol until the user hovers over it, at which point you can display a popup box that has some custom information within it, typically this would be things like the site name, any access information, number of alarms, whether telemetry is healthy, whether mains power is healthy.. those 'site critical' items.

Of course you may have a number of maps that display different information, for example a zone metering map might show flowmeters / pressure meters with their relevant information (flow rates / totalised daily flow / current, min, max pressure etc)

 

As an idea of the kind of out-of-the-box base maps you can have, here are some examples from ArcGIS Online.

The Satellite view

ArcGISOnline.png

 

The topographical

ArcGISTopological.png

 

You can also use Bing Maps, Open Street Maps etc, which can provide road / land plot information at higher zoom levels.

 

 

Then you can add overlays, which are just any WMS data source.  It would be technically possible to create your own WMS data to have custom graphics as you like... but here's some that are available directly (targeting AU.. but the UK likely has similar sources available).

Obviously here in Australia fire is a serious issue, especially for water/waste water assets that might require emergency servicing to be performed during fire danger periods and in remote areas.  So providing this information to the operations staff as part of the SCADA platform has significant benefits.

 

Fire Danger Rating (there are a few options for time periods available.. like Today, Tomorrow, This week I believe..)

FireDangerRating.png

 

Rain Radar (again with options for time periods..)

RainRadar.png

 

Sentinel Hotspot Satellite.  This satellite just looks at temperatures across AU, and if there is a 'hot spot' it puts a symbol of a fire there related to how hot it might be.  It's a way used to identify rapid onset fires (although it's pretty hit and miss as to whether it is indeed a fire).

SentinelHotspot.png

 

 

If using ViewX on a device which is location aware, or using the MobileApp then it's possible for user locations to also be plotted on such a map.  Again for remote worker monitoring this can be incredibly useful (although it can be a concern in regards to worker surveillance.. no one wants to have 'eyes' on them all the time they are at work).

 

There are quite a few 'features' that are lacking in the existing mapping implementation, but this is where lodging well considered feature requests with your local Tech Support contacts is advisable.  If you don't tell Schneider what you want in the product, you can't expect them to add it in..


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • geospatial
  • mapping
  • WMS
Reply

Link copied. Please paste this link to share this article on your social media post.

Simon_Lee
Simon_Lee Cadet
Cadet

Posted: ‎2020-02-05 02:42 PM

0 Likes
3
3501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-05 02:42 PM

Thanks for all the responses so far. What I am really after is examples of features that have been implemented that were not possible without the Geo features of the latest software, i.e. what Use Cases do you have for the Geo Location or Mapping features?

 

I work for Schneider and so understand the technicalities of how to configure the system using location data etc. and also the limitations with these features (although some of those in the replies are very useful information!)

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-05 02:52 PM

In response to Simon_Lee
0 Likes
2
3499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-05 02:52 PM

The rain radar / fire danger overlays are about the only things we couldn't easily do in ViewX natively before.

We were able to launch a web browser with a particular URL path which provided 'something', but it wasn't as nicely integrated with the site locations as can be done now.

 

There's a number of customers that have these maps configured within Victoria (in the water/waste water space).

I would say probably around half a dozen or so that I've been involved with.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Simon_Lee
Simon_Lee Cadet
Cadet

Posted: ‎2020-02-06 01:07 AM

In response to BevanWeiss
0 Likes
1
3487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-06 01:07 AM

Thanks for the detailed replies. I think Rain Radar is the most likely use case for our water/wastewater customers. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-06 01:13 AM

In response to Simon_Lee
0 Likes
0
3484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-06 01:13 AM

It really comes down to what data sources you have available in the UK...

 

Obviously water catchments might be another option... overlaying Rain Radar and Water Catchment outlines would be useful to determine how much inflow an open reservoir might get or similar.

 

I was trying to push Schneider (nor Aveva) to provide some programmatic access (from within the ClearSCADA server) to the raster data associated with a WMS result.  The thinking here was that with a defined 'catchment' and something like the forecast rain radar it would be possible to roughly calculate an expected infiltration flow on sewer pump stations and preemptively pump certain high risk stations down.  Unfortunately nothing came of it.

 

Looking here

https://www.bgs.ac.uk/data/services/wms.html

it seems there's a few geology options, which might be useful in the event of heavy rain to identify potential flash flood environments (clay laden soil / high water table etc).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore