New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Printing .xlsx Fiile from Citect Scada on trigger
EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-3010:08 PM
Printing .xlsx Fiile from Citect Scada on trigger
I need to print .xlsx file from printer on trigger as per defined size . Please help me how to add device or what settings required. I have done printing .csv file and also .rtf File (in reports) by using below command in cicode
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-1708:41 PM
You'll need to work out a command line to print an Excel file, and then pass it to either the SYSTEM() logic function, or to the System command pick action.
You could instantiate an Object instance for Excel within ViewX... but that requires a client to do it... so it's not applicable for 'on a trigger'.
Lead Control Systems Engineer for Alliance Automation (VIC). All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..