Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Open mimic in Virtual ViewX

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Open mimic in Virtual ViewX
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
IvanDeMarco97
Lieutenant JG IvanDeMarco97 Lieutenant JG
Lieutenant JG

Posted: ‎2023-06-08 05:46 AM

1 Like
10
3301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-08 05:46 AM

Open mimic in Virtual ViewX

Hi all,
I need to open a specific mimic from a URL in Virtual ViewX, is it possible to do that? Is there any way to do this?

 

Thank you!

Labels
  • Labels:
  • Mimics
  • SCADA
  • Virtual ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
SurprisedEwe1
Ensign SurprisedEwe1
Ensign

Posted: ‎2024-11-24 10:31 PM

0 Likes
1
2264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-24 10:31 PM

Has this functionality been implemented, and if so how is it used?  I am about to be engaged in a project that others had previously enquired about this functionality and they had received an email (in April 2024) that was forwarded to me. This was the response from Schneider:

 

"There is a new feature in ViewX, where /openobject:[system:]name on the command line will open the database object 'name' with optional system name. This can be used in Virtual ViewX by adding a URL parameter.

To make this work the 'Allow Browser Arguments' checkbox is ticked in the VVX Server, and the URL becomes

http://localhost:85/?/openobject:%22Opening%20Page%22 "

 

I have downloaded the latest versions of Geo SCADA 2021 and 2023 (client is currently running 2021, but have checked functionality on both) and found in the Release Notes the information regarding this "openobject" option.

 

Using the demo project I have successfully had the ViewX shortcut open a mimics with a command such as:

"...\SE.Scada.ViewX.exe" /openobject:"Presentation.Product Life Cycle"

 

The equivalent URL for Virtual ViewX below, however, requests user credentials but then does not load any mimic: http://localhost:85/?/openobject:"Presentation.Product Life Cycle"

 

I have confirmed that the "Allow Browser Arguments" field is set for the Virtual ViewX application in the Virtual ViewX Manager.  Any other suggestions as this functionality is critical to the viability of our project?

 

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-12-12 03:15 AM

0 Likes
0
2134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-12 03:15 AM

My answers:

Is it possible to open an AlarmList of a Group? - No, but if you have a mimic with the alarm list on it, then display that mimic.

Is it possible to enter the username and password to access directly in the url? No. As Geoff wrote, you could use the Guest user.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
geoffpatton
Captain geoffpatton
Captain

Posted: ‎2023-06-08 07:42 AM

0 Likes
0
3298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-08 07:42 AM

I assume that you want users to go to a specific Mimic after they login.

You can set the user's home page to that mimic and select load home page on login.

Reply

Link copied. Please paste this link to share this article on your social media post.

IvanDeMarco97
Lieutenant JG IvanDeMarco97 Lieutenant JG
Lieutenant JG

Posted: ‎2023-06-11 11:11 PM

0 Likes
0
3282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-11 11:11 PM

Not exactly, once the user has logged in, from another program I'd like to open any page directly...

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2023-06-12 07:02 AM

0 Likes
0
3272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-12 07:02 AM

Virtual ViewX is basically just ViewX encapsulated in a HTML5 wrapper so you cannot just externally open a URL and load a mimic. It might be possible to engineer something using the undocumented ViewX automation interface but I do not really think it will work since Virtual ViewX sessions share the same ViewX. If you want to try using it not supported so support will not help. This might be helpful https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/ViewX-API-Documentation/m-p/414897 and there are a few other post on here you can search for too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Killultagh
Lieutenant JG Killultagh
Lieutenant JG

Posted: ‎2023-09-27 08:56 AM

0 Likes
0
2925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-27 08:56 AM

Hi all

 

I also have this question as well from a customer who currently has WebX URL's attributed to PowerBI dashboards however, with the transition to VVX the direct link to mimics and trends now appears to be no longer available?

 

Is there a workaround?

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2023-10-02 01:05 AM

1 Like
0
2894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-02 01:05 AM

Hi All,

this functionality - adding the mimic name into a URL to Virtual ViewX - is not available right now but is being considered for development and release. More news when we have it!

Steve

 

Reply

Link copied. Please paste this link to share this article on your social media post.

SurprisedEwe1
Ensign SurprisedEwe1
Ensign

Posted: ‎2024-11-24 10:31 PM

0 Likes
1
2265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-24 10:31 PM

Has this functionality been implemented, and if so how is it used?  I am about to be engaged in a project that others had previously enquired about this functionality and they had received an email (in April 2024) that was forwarded to me. This was the response from Schneider:

 

"There is a new feature in ViewX, where /openobject:[system:]name on the command line will open the database object 'name' with optional system name. This can be used in Virtual ViewX by adding a URL parameter.

To make this work the 'Allow Browser Arguments' checkbox is ticked in the VVX Server, and the URL becomes

http://localhost:85/?/openobject:%22Opening%20Page%22 "

 

I have downloaded the latest versions of Geo SCADA 2021 and 2023 (client is currently running 2021, but have checked functionality on both) and found in the Release Notes the information regarding this "openobject" option.

 

Using the demo project I have successfully had the ViewX shortcut open a mimics with a command such as:

"...\SE.Scada.ViewX.exe" /openobject:"Presentation.Product Life Cycle"

 

The equivalent URL for Virtual ViewX below, however, requests user credentials but then does not load any mimic: http://localhost:85/?/openobject:"Presentation.Product Life Cycle"

 

I have confirmed that the "Allow Browser Arguments" field is set for the Virtual ViewX application in the Virtual ViewX Manager.  Any other suggestions as this functionality is critical to the viability of our project?

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Killultagh
Lieutenant JG Killultagh
Lieutenant JG

Posted: ‎2024-11-26 01:22 AM

In response to SurprisedEwe1
0 Likes
0
2233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-26 01:22 AM

I can confirm that the URL feature is available in the latest release however, it does not work with trend objects which is disappointing.

Reply

Link copied. Please paste this link to share this article on your social media post.

IvanDeMarco97
Lieutenant JG IvanDeMarco97 Lieutenant JG
Lieutenant JG

Posted: ‎2024-12-11 01:56 AM . Last Modified: ‎2024-12-11 06:22 AM

0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-11 01:56 AM . Last Modified: ‎2024-12-11 06:22 AM

Two questions:

Is it possible to open an AlarmList of a Group?

Is it possible to enter the username and password to access directly in the url?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2024-12-11 08:07 AM

0 Likes
0
2155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-11 08:07 AM

I have not tried setting any VVX links to specific objects so I don't know the answer. I also don't currently have access to a VVX server.

However this might help with the login part of your question.

There is a setting in the Virtual ViewX Manger that lets you turn off loading the login when you first connect. As long as you are inside you network that likely won't be a problem. If everyone is allowed to View and all you need is viewing rights for what you are doing, that may take care of the login.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-12-12 03:15 AM

0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-12 03:15 AM

My answers:

Is it possible to open an AlarmList of a Group? - No, but if you have a mimic with the alarm list on it, then display that mimic.

Is it possible to enter the username and password to access directly in the url? No. As Geoff wrote, you could use the Guest user.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.