MQTT string to value

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re: MQTT string to value
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
308
AndrewScott
Admiral AndrewScott
98
BevanWeiss
Spock BevanWeiss
91
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
37
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
niejan
Crewman niejan
Crewman

Posted: ‎2025-01-08 03:28 AM

0 Likes
2
526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-08 03:28 AM

MQTT string to value

Hello all, best wishes in new year.

I have simple questions

Q1 - is there any way how to force Json A to accept string

Q2 - is there any way how to force Json A to convert published value as a string and covert it into number?

 

Description of my problem

I have JSON that looks like that

 

{
"main":
{
"value": "868.9640",
"raw": "00868.9640",
"pre": "868.9640",
"error": "no error",
"rate": "0.000060",
"timestamp": "2024-12-18T18:27:05+0100"
}

}

 

And i want to receive the tag VALUE. But its represented as a string. And there is no string point in CSE 2022 (23 update 85.8650) and analog point is not accepting that format. While HomeAssistant has no problem with that (but i am not using that).

My Mqtt broker is Mosquitto as i found big help in one of Steve's videos on youtube.

When i used Mqtt browser and force to pretend that he received the JSON in this format

 

{
"main":
{
"value": 868.9640,
"raw": "00868.9640",
"pre": "868.9640",
"error": "no error",
"rate": "0.000060",
"timestamp": "2024-12-18T18:27:05+0100"
}

}

 

I can get the value into analog point easily.

Labels
  • Labels:
  • Drivers
  • IoT
  • SCADA
  • Tags:
  • english
  • mqtt
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2025-01-08 07:39 AM

0 Likes
0
506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-08 07:39 AM

Sorry, no. But the new Text/JSON driver in Geo SCADA 2023 might do it?

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2025-01-08 07:39 AM

0 Likes
0
507
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-08 07:39 AM

Sorry, no. But the new Text/JSON driver in Geo SCADA 2023 might do it?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

niejan
Crewman niejan
Crewman

Posted: ‎2025-01-09 02:02 AM . Last Modified: ‎2025-01-10 12:49 AM

0 Likes
0
480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-09 02:02 AM . Last Modified: ‎2025-01-10 12:49 AM

Ok, i'll give a try

 

EDIT:

yes the new driver helped and work with strings. Now i can easily convert the string into value. Thank you Mr Steve.

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of