ViewX not running on server after upgrade from GeoSCADA 2020 to GeoSCADA 2022

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • ViewX not running on server after upgrade from GeoSCADA 2020 to GeoSCADA 2022
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
kerro74
Crewman kerro74
Crewman

Posted: ‎2023-05-30 08:28 PM

0 Likes
9
1901
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-30 08:28 PM

ViewX not running on server after upgrade from GeoSCADA 2020 to GeoSCADA 2022

Upgraded GeoSCADA today and all appeared to go well. However, when I start ViewX I get the initial splash screen the it shuts down. Upgraded client and ViewX on client works fine. I have attached the ViewX log file.

 

Snapshot of error below

2023-05-31 02:48:45.201 Default [1ED8:01] [PrismModule] RegisterTypes (ViewX.Database) : OUT
2023-05-31 02:48:45.201 Default [1ED8:01] [PrismModule] OnInitialized (ViewX.Database) : IN
2023-05-31 02:48:45.253 Default [1ED8:01] [PrismModule] OnInitialized (ViewX.Database) : OUT
2023-05-31 02:48:45.253 Default [1ED8:01] [PrismModule] RegisterTypes (ViewX.Favorites) : IN
2023-05-31 02:48:45.253 Default [1ED8:01] [PrismModule] RegisterTypes (ViewX.Favorites) : OUT
2023-05-31 02:48:45.253 Default [1ED8:01] [PrismModule] OnInitialized (ViewX.Favorites) : IN
2023-05-31 02:48:45.253 Default [1ED8:01] [PrismModule] OnInitialized (ViewX.Favorites) : OUT
2023-05-31 02:48:45.253 Default [1ED8:01] [PrismModule] RegisterTypes (ViewX.HelpViewer) : IN
2023-05-31 02:48:45.253 Default [1ED8:01] [PrismModule] RegisterTypes (ViewX.HelpViewer) : OUT
2023-05-31 02:48:45.262 Default [1ED8:01] [PrismModule] OnInitialized (ViewX.HelpViewer) : IN
2023-05-31 02:48:45.430 Default [1ED8:01] [System.Windows.Application] Uncaught Exception
*** Prism.Modularity.ModuleInitializeException: An exception occurred while initializing module 'ViewX.HelpViewer'.
- The exception message was: The type initializer for 'SchneiderElectric.Scada.ViewX.CefSharp.CefSharpInitializer' threw an exception.
- The Assembly that the module was trying to be loaded from was:SE.Scada.ViewX.HelpViewer, Version=6.85.8390.1, Culture=neutral, PublicKeyToken=9e16b9dd55e2cd53
Check the InnerException property of the exception for more information. If the exception occurred while creating an object in a DI container, you can exception.GetRootException() to help locate the root cause of the problem. ***
at Prism.Modularity.ModuleInitializer.HandleModuleInitializationError(IModuleInfo moduleInfo, String assemblyName, Exception exception)
at Prism.Modularity.ModuleInitializer.Initialize(IModuleInfo moduleInfo)
at Prism.Modularity.ModuleManager.LoadModulesThatAreReadyForLoad()
at Prism.Modularity.ModuleManager.LoadModuleTypes(IEnumerable`1 moduleInfos)
at Prism.Modularity.ModuleManager.LoadModulesWhenAvailable()
at Prism.Modularity.ModuleManager.Run()
at SchneiderElectric.ApplicationFramework.UI.BaseApplication.InitializeModules()

Attachments
SE.Scada.ViewX.exe_Session1.log
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
kerro74
Crewman kerro74
Crewman

Posted: ‎2025-01-08 08:42 PM

In response to dahoodman
0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-08 08:42 PM

I tried all ways mentioned but did not resolve the issue at the time. I ran up a new VM onto the server and ran the install again. Was only a small plant so the impact was not too significant at the time.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
dahoodman
Ensign dahoodman
Ensign

Posted: ‎2024-11-19 11:14 AM

0 Likes
1
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-19 11:14 AM

Did you ever find a solution to your problem? We have a similar issue that ViewX won't fully load but on 2021. We aren't sure when it started so we don't know if it started when we upgraded from 2020 to 2021 or perhaps after we applied the Dec 2023 updates of 2021 or maybe a MS Update. Interested to know what you found out.

Reply

Link copied. Please paste this link to share this article on your social media post.

tfranklin
Commander tfranklin
Commander

Posted: ‎2024-11-20 05:39 AM

0 Likes
1
1587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-20 05:39 AM

There was a version somewhere near there that had an issue with ViewX upgrades related to CEFSharp files not getting cleaned up properly.  I think the CEFSharp files moved from the base location into a nested folder for \Modules\, but there was one release that didn't clean up the old files. 

 

Check and see if there are any files that start with CEFSharp in the base C:\Program Files (x86)\Schneider Electric\ClearSCADA\ folder.  Validate there are CEFSharp files in the \Modules\ folder.  If there are are CEFSharp in the Modules folder AND also in the base folder, close ViewX, and then delete them from the base folder. 

 

Other option is to fully uninstall/reinstall, but that's a little more aggressive. 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-11-21 01:33 AM

0 Likes
1
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 01:33 AM

What Trent wrote!

 

Also, after removing any files you can do a Repair install.

 

Also - are you sure you:

a) Didn't have Virtual ViewX Server installed, or

b) Did have Virtual ViewX Server installed and you upgraded it too.

If you did have Virtual ViewX Server installed and you did not upgrade it, you can have a similar problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

dahoodman
Ensign dahoodman
Ensign

Posted: ‎2024-11-21 04:07 AM

In response to sbeadle
0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 04:07 AM

I don't believe our version 2021 Dec 2023 Update has Virtual ViewX as an option. I just ran the ISO and tried to modify to see if it was even available. We don't use it, plus this happened on all 3 servers (Main Standby and Perm Standby) and no clients. I was thinking it must have been a MS Update or something or maybe even Symantec Endpoint Protection. I did try what Trent suggested and even did a repair. I wasn't sure I wanted to go as far as a complete remove and reinstall. We have plans to upgrade our servers to Server 2022 and GeoSCADA 2023. We typically don't run it on the server, but every now and then when we go to delete a tag we have to be Super User and you can only [apparently] log in as SU on Main. We wanted to get rid of Super User but are a tad worried that if we do then when we run across a tag that requires SU to remove that we'd be stuck. Perhaps when we install 2023 we will see about eliminating it. 

Reply

Link copied. Please paste this link to share this article on your social media post.

dahoodman
Ensign dahoodman
Ensign

Posted: ‎2024-11-21 04:08 AM

In response to tfranklin
0 Likes
0
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 04:08 AM

Thank you for that answer. Unfortunately it was not the case for us. 

Reply

Link copied. Please paste this link to share this article on your social media post.

gabarit
Lieutenant JG gabarit
Lieutenant JG

Posted: ‎2024-11-21 11:58 PM

0 Likes
1
1536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 11:58 PM

I have encountered this problem many times when I upgraded to a new version of the product.
This is resolved by uninstalling ViewX and reinstalling it or Repair.

Reply

Link copied. Please paste this link to share this article on your social media post.

dahoodman
Ensign dahoodman
Ensign

Posted: ‎2024-11-25 02:52 AM

In response to gabarit
0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-25 02:52 AM

Yeah the re-install may be our next option. We tried the repair already. Since it's all three of our servers we were hoping to not have to uninstall and re-install. We need to upgrade anyway so I guess this is as good a time as any I guess.

Reply

Link copied. Please paste this link to share this article on your social media post.

kerro74
Crewman kerro74
Crewman

Posted: ‎2025-01-08 08:42 PM

In response to dahoodman
0 Likes
0
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-08 08:42 PM

I tried all ways mentioned but did not resolve the issue at the time. I ran up a new VM onto the server and ran the install again. Was only a small plant so the impact was not too significant at the time.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2025-01-10 02:20 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-10 02:20 AM

Thanks for your comments - there may have been some other software/install interfering, perhaps one using a shared component? If this repeats the support team could help - perhaps by examining the installed files in more detail. (Though in the heat of an upgrade I understand it's commercially expedient to nuke it and reinstall to meet timescales!)

 

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore