Posted: 2023-01-05 08:42 PM
I found it. The Promote under the Control tab need to be enabled. Thanks
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-05 01:59 AM
You've not specified which driver (Modbus, DNP3, IEC 60870-5 etc.) you're using. In general, create an output point (e.g. DNP3 Binary Output), however for drivers that don't have separate input & output points just enable controls on the point.
Andrew Scott, R&D Principal Technologist, AVEVA
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-05 07:00 PM
Hi Andrew, thanks for your reply. Currently I use Modbus, I can read the value of the register ( e.g. 40001), but I can't change the value of it.
- Tags:
- Geo SCADA
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-05 08:42 PM
I found it. The Promote under the Control tab need to be enabled. Thanks
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-06 01:34 AM
I think you're mistaken. The Promote feature allows you to automatically promote scanning (to a faster rate) on selected outstation(s) when you control a point, to get feedback from the consequences of the control more quickly.
To write to a Modbus holding register you need to configure either a Modbus Generic Analog Output Point or Modbus Generic Digital Output Point and then use the Control method to perform the write.
Andrew Scott, R&D Principal Technologist, AVEVA