Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Database lock Alarm

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re: Database lock Alarm
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Janeway sbeadle Janeway
217
BevanWeiss
Spock BevanWeiss
81
AndrewScott
Captain AndrewScott
54
AdamWoodland
Commander AdamWoodland Commander
23
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
jleon
Ensign jleon
Ensign

Posted: ‎2020-10-14 08:43 AM . Last Modified: ‎2023-05-03 12:08 AM

0 Likes
2
1399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-10-14 08:43 AM . Last Modified: ‎2023-05-03 12:08 AM

Database lock Alarm

I have a system that remains with a high database lock percentage. The alarm is active almost all time.
What causes this alarm?

Labels
  • Labels:
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AdamWoodland
Commander AdamWoodland Commander
Commander

Posted: ‎2020-10-14 04:31 PM . Last Modified: ‎2023-02-06 10:29 PM

0 Likes
1
1389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-10-14 04:31 PM . Last Modified: ‎2023-02-06 10:29 PM

The quick answer is "it is usually logic or file flushing to disk", so check you don't have some crazy logic running too much (Queries -> Logic Execution Status) and that you have anti-virus definitions configured correctly as per https://community.exchange.se.com/t5/Geo-SCADA-Knowledge-Base/bg-p/geo-scada-knowledge-base

 

So, with wild speculation aside, if you're running a version released in the past couple of years you get some funky lock analysis tools. You can enable LCK/Lock logging in the DB log files since forever but this new function does a pivot table on that so is much better for identifying the effect and then you can drill down through the logs for the cause.

 

What I recommend is:

 

1. Go to Server Status

2. Go to General -> Logging

3. Enable LCK/Lock logging (note this will drastically increase the amount of logging on your system which may impact performance and will cause DB log files to roll over much quicker, so make sure you have sufficient DB logs configured)

4. Still in Server Status go to Database -> Lock Diagnostic Read and also Write (in recent versions its two windows, previous version it was one). Right click on each one and choose "Enable Diagnostics"

5. Let it run for a bit (probably not too long in your case given you said always active)

6. Check out the screen for anything which is...

 

 a. Longest [Read|Write] Lock is > 1000mS

 b. [Read|Write] Locks Per Second is > 1 (note that things like InterestThread are probably more than 1, depends on what clients you have an what they're doing)

 

7. There might be something obvious, but I'd recommend you open a support case with the logs and then they can take a closer look (you will need to provide the DB logs with LCK logging enabled and DBSnaphot files which capture some of these Lock Diagnostics in)

8. When you aren't looking at it, disable LCK logging. The Diagnostic tabs you can leave as necessary.

 

There is a setting to reset the Diagnostics tab each snapshot, its probably not that useful for this short time frame analysis but support may ask for it.

 

Just for some info. The difference between read and write locks is you can only have one write lock active on a system, but you can have multiple read locks active concurrently. You can't have read and write locks active at the same time. This makes write locks very dangerous if they get out of control and are usually the cause of the system locking up for periods of time.

 

There are some "read" actions that are done under read locks for very specific reasons. Flushing data to disk is a write lock and so when anti-virus starts to interfere with the file writes that can have a serious effect.

 

If you have a high lock alarm but you're not having the system lock up you're probably looking at lots of read locks happening.

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Reply
Replies 2
AdamWoodland
Commander AdamWoodland Commander
Commander

Posted: ‎2020-10-14 04:31 PM . Last Modified: ‎2023-02-06 10:29 PM

0 Likes
1
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-10-14 04:31 PM . Last Modified: ‎2023-02-06 10:29 PM

The quick answer is "it is usually logic or file flushing to disk", so check you don't have some crazy logic running too much (Queries -> Logic Execution Status) and that you have anti-virus definitions configured correctly as per https://community.exchange.se.com/t5/Geo-SCADA-Knowledge-Base/bg-p/geo-scada-knowledge-base

 

So, with wild speculation aside, if you're running a version released in the past couple of years you get some funky lock analysis tools. You can enable LCK/Lock logging in the DB log files since forever but this new function does a pivot table on that so is much better for identifying the effect and then you can drill down through the logs for the cause.

 

What I recommend is:

 

1. Go to Server Status

2. Go to General -> Logging

3. Enable LCK/Lock logging (note this will drastically increase the amount of logging on your system which may impact performance and will cause DB log files to roll over much quicker, so make sure you have sufficient DB logs configured)

4. Still in Server Status go to Database -> Lock Diagnostic Read and also Write (in recent versions its two windows, previous version it was one). Right click on each one and choose "Enable Diagnostics"

5. Let it run for a bit (probably not too long in your case given you said always active)

6. Check out the screen for anything which is...

 

 a. Longest [Read|Write] Lock is > 1000mS

 b. [Read|Write] Locks Per Second is > 1 (note that things like InterestThread are probably more than 1, depends on what clients you have an what they're doing)

 

7. There might be something obvious, but I'd recommend you open a support case with the logs and then they can take a closer look (you will need to provide the DB logs with LCK logging enabled and DBSnaphot files which capture some of these Lock Diagnostics in)

8. When you aren't looking at it, disable LCK logging. The Diagnostic tabs you can leave as necessary.

 

There is a setting to reset the Diagnostics tab each snapshot, its probably not that useful for this short time frame analysis but support may ask for it.

 

Just for some info. The difference between read and write locks is you can only have one write lock active on a system, but you can have multiple read locks active concurrently. You can't have read and write locks active at the same time. This makes write locks very dangerous if they get out of control and are usually the cause of the system locking up for periods of time.

 

There are some "read" actions that are done under read locks for very specific reasons. Flushing data to disk is a write lock and so when anti-virus starts to interfere with the file writes that can have a serious effect.

 

If you have a high lock alarm but you're not having the system lock up you're probably looking at lots of read locks happening.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Reply
jleon
Ensign jleon
Ensign

Posted: ‎2020-11-11 05:50 AM

In response to AdamWoodland
0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-11-11 05:50 AM

Thanks Adam, your information very useful. I was checking and testing the last month.

 

We have a external application that querie the database, that was the reason of high percentage databaselock.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc