Hello,
I get datas in Geo SCADA with RTU in Geo SCADA Expert 2021 but i have a problem. When there is no communication, data isn't buffered so I can not receive the data afterwards. Datas are stored in RTU, but not sent to SCADA. I think the RTU settings are correct, but i don't find the correct settings in Geo SCADA. Can you help me about this problem?
I'm sharing some screenshots about my setting screen.
This is the setting screen i made in RTU.
This is the setting screen i made in Geo SCADA. I don't understand what to do here.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-18 03:57 AM
You've not stated what RTU you're using or even what driver / protocol is being used.
How do you know the RTU is storing the buffered data? Does it have some kind of diagnostics to show what it is storing?
If the RTU isn't sending the buffered data to Geo SCADA then the problem is likely with the RTU. Have you examined the comms log to see what the RTU is actually sending to Geo SCADA?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-21 10:24 AM
@AndrewScott, @abdullah123456789 asked a earlier question that this is really a continuation of. https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/Data-Buffering/td-p/410403
@abdullah123456789it is easier for you to get answers if you keep asking questions in the same thread, or if you feel you really must start a new thread then to post a link to the existing related thread.
I looking at the screenshots you provided I suggest you try selecting the significant change check box on your historical data filter.
You only have current data check which means that it is only going to log the current values logged at the time of the poll.
So hopefully that gets your RTU stored data into the historian.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-23 10:57 PM
I will try this. Thanks for help.