Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Data Buffering Problem

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Data Buffering Problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
abdullah123456789
abdullah123456789
Explorer

Posted: ‎2022-11-18 03:46 AM . Last Modified: ‎2023-05-02 11:50 PM

0 Likes
3
1471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-18 03:46 AM . Last Modified: ‎2023-05-02 11:50 PM

Data Buffering Problem

Hello,

 

I get datas in Geo SCADA with RTU in Geo SCADA Expert 2021 but i have a problem. When there is no communication, data isn't buffered so I can not receive the data afterwards. Datas are stored in RTU, but not sent to SCADA. I think the RTU settings are correct, but i don't find the correct settings in Geo SCADA. Can you help me about this problem?

 

I'm sharing some screenshots about my setting screen.

 

This is the setting screen i made in RTU.

4921684d-893c-45fb-81f9-8bea7831f6e8.png

 

This is the setting screen i made in Geo SCADA. I don't understand what to do here.

2.PNG3.PNG

Labels
  • Labels:
  • RTU
  • SCADA
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
AndrewScott
AndrewScott
Leader

Posted: ‎2022-11-18 03:57 AM

0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-18 03:57 AM

You've not stated what RTU you're using or even what driver / protocol is being used.

 

How do you know the RTU is storing the buffered data? Does it have some kind of diagnostics to show what it is storing?

 

If the RTU isn't sending the buffered data to Geo SCADA then the problem is likely with the RTU. Have you examined the comms log to see what the RTU is actually sending to Geo SCADA?


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
geoffpatton
Leader

Posted: ‎2022-11-21 10:24 AM

0 Likes
1
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-21 10:24 AM

@AndrewScott, @abdullah123456789 asked a earlier question that this is really a continuation of. https://community.se.com/t5/EcoStruxure-Geo-SCADA-Expert/Data-Buffering/td-p/410403

 

@abdullah123456789it is easier for you to get answers if you keep asking questions in the same thread, or if you feel you really must start a new thread then to post a link to the existing related thread.

 

I looking at the screenshots you provided I suggest you try selecting the significant change check box on your historical data filter.

You only have current data check which means that it is only going to log the current values logged at the time of the poll.

So hopefully that gets your RTU stored data into the historian.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

abdullah123456789
abdullah123456789
Explorer

Posted: ‎2022-11-23 10:57 PM

In response to geoffpatton
0 Likes
0
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-23 10:57 PM

I will try this. Thanks for help.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore