ClearSCADA incoming SMS

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • ClearSCADA incoming SMS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
318
AndrewScott
Admiral AndrewScott
109
BevanWeiss
Spock BevanWeiss
96
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
donalselmanaj
donalselmanaj
Cadet

Posted: ‎2020-06-16 02:32 PM . Last Modified: ‎2023-05-03 12:14 AM

0 Likes
6
2975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-16 02:32 PM . Last Modified: ‎2023-05-03 12:14 AM

ClearSCADA incoming SMS

Hello,

 

How can I read incoming SMS text in ClearSCADA from e 3rd party device?

 

I have connected ClearSCADA with an Ultra eSAM modem. I can send SMS from ClearSCADA to a cellphone number but incoming SMS does not work.

 

Thank you.

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-06-17 05:01 AM

0 Likes
2
2948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-17 05:01 AM

I suspect out of the box the eSAM won't handle incoming SMS.

You would need to turn off SMS Management on the radio modem itself, and potentially change where the URC messages get sent (since given the eSAM, I suspect you're using AT over TCP.. and the default setting of these modems is typically to not send URC over this interface).

 

I've currently got some similar modems (Robustel R2000-4L) doing self-testing where they send themselves an SMS every few hours to confirm that the entire loop is working.

 

As noted by the others, you should follow the how-to, and really even just get it all working from the AT command line without ClearSCADA involved first.  If you can use the AT command line to send, and receive an SMS, then getting ClearSCADA to do it shouldn't be too much of a problem.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
geoffpatton
Captain geoffpatton
Captain

Posted: ‎2020-06-16 03:02 PM . Last Modified: ‎2023-04-25 03:46 AM

0 Likes
1
2969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-16 03:02 PM . Last Modified: ‎2023-04-25 03:46 AM

Maybe this will help. I've only seen this done once years ago.

 

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Supported-Interface-and-Protocol-Versions/ba-p/...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-06-17 03:07 AM

In response to geoffpatton
0 Likes
0
2958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-17 03:07 AM

Perhaps get the modem's supported commands. In the Resource Center page:

 

'The modes supported by a modem can be queried using the "AT+CNMI=?" command (without the quotes) from a VT terminal.'

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-06-17 05:01 AM

0 Likes
2
2949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-17 05:01 AM

I suspect out of the box the eSAM won't handle incoming SMS.

You would need to turn off SMS Management on the radio modem itself, and potentially change where the URC messages get sent (since given the eSAM, I suspect you're using AT over TCP.. and the default setting of these modems is typically to not send URC over this interface).

 

I've currently got some similar modems (Robustel R2000-4L) doing self-testing where they send themselves an SMS every few hours to confirm that the entire loop is working.

 

As noted by the others, you should follow the how-to, and really even just get it all working from the AT command line without ClearSCADA involved first.  If you can use the AT command line to send, and receive an SMS, then getting ClearSCADA to do it shouldn't be too much of a problem.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

donalselmanaj
donalselmanaj
Cadet

Posted: ‎2020-06-22 01:16 PM

In response to BevanWeiss
0 Likes
1
2913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-22 01:16 PM

It was actually a firmware problem as eSAM with the "out-of-the-box" firmware was not able to manage incoming SMS.

 

Thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-06-22 04:09 PM

In response to donalselmanaj
0 Likes
0
2908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-22 04:09 PM

@donalselmanaj Can you perhaps detail which firmware version did NOT work, and which one DID work?

That will help others from wondering what they're doing wrong 🙂

 

I do vaguely remember something similar quite a few years ago, although I can't remember the version numbers either.

From memory it was almost an entire 'series' difference in firmware, I think it shipped with like a 1.xx firmware, and the updated firmware was a 2.xx (NOTE: absolutely do NOT trust these numbers...).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Technical
Technical
Cadet

Posted: ‎2023-02-06 08:38 PM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-06 08:38 PM

Hi All,

 

Just to update you all, Ultra eSAM support incoming and outgoing SMS. For user guide and further information please contact "Intercel". online@intercel.com.au 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore