Posted: 2023-02-06 07:00 AM . Last Modified: 2023-05-02 11:48 PM
I want to take the result of a query and write that result to an Internal Point. I have structured the query to return a single value, but I am unsure of how to map this to an internal tag. I assume I can accomplish this in ST, but I am having difficulty with how to code it.
Any help would be appreciated!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-07 01:30 AM
The ODBC driver is specifically designed to map the result of a query onto a point, see Introduction to the ODBC Driver in the help. This driver has its own points rather than using internal points.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-07 01:30 AM
The ODBC driver is specifically designed to map the result of a query onto a point, see Introduction to the ODBC Driver in the help. This driver has its own points rather than using internal points.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-07 07:02 AM
Exactly what I needed, thank you!