ClearSCADA: external data to Historian at regular intervals

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

Solved
nosaj
Ensign
Ensign
0 Likes
5
1341

ClearSCADA: external data to Historian at regular intervals

Hi All

 

There have been some similar questions [1], but I haven't found one that quite matches my use case.

 

* we are using the site ClearSCADA 2017 R3 historical data for reporting: summary, performance metrics, etc.

* the site ClearSCADA historical data is also used as a data concentrator for the national headquarters.

* we'd like to push report results back into the ClearSCADA historical database. Writing to live data is not preferred - the reports happen up to a day later, so pushing timestamped values back is very much preferred to time-of-data-arrival timestamps, i.e. if the data is pushed back in at 8 pm and shows values that happened at 2 pm, we'd like the values to be recorded as happening at 2 pm rather than 8 pm.

* if possible, it would also be good to be able to back-fill report data for several months. I believe there might be complications with this, however.

 

Currently we are pulling data from the database using the ODBC driver, querying CDBHistoric. However, CDBHistoric is read-only from ODBC (makes sense), so we need another way to get the data in.

 

Does anyone know if any of these work?

 

* ODBC to push timestamped historical data to a different table?

* Web API?

* Other scripting languages?

 

The only issue with the solution in the footnote is it's meant for manual data loading when someone clicks a mouse (deal-breaker) and is only good for data up to around 2 weeks old (not a deal-breaker). We need it to happen without user input e.g. every day at 6 am. Not clear if that's easy / possible / etc. Happy to RTFM, if someone could point me to the FM.  🙂

 

Thanks in advance

 

Jason

 

 

[1] https://community.exchange.se.com/t5/Geo-SCADA-Expert-Forum/Imported-CDBHISTORIC-table-SELECT-INSERT...


Accepted Solutions
AdamWoodland
Commander Commander
Commander
0 Likes
0
1288
5 Replies 5
geoffpatton
Commander
Commander
0 Likes
1
1328

Re: ClearSCADA: external data to Historian at regular intervals

Are you sure you can't write to it from ODBC, if your ODBC connected program is logged in with a user that has the right to edit history?

 

You can do this using the .net api. You could simply have a Windows task Scheduled the runs you program, or make your program run all the time and check for the file update.

 

We have a program that imports history and it is run all the time. It checks if the input file timestamp has changed and when it has it processes the data.

 

I really don't know the details of how the data is loaded into the history, I did not write the program.

BevanWeiss
Spock
Spock
0 Likes
1
1310

Re: ClearSCADA: external data to Historian at regular intervals

What are the 'report results'?

From the way that you've currently described it, you have all this data in the ClearSCADA server, and then you send it to national headquarters for reporting... but then all the data should already existing in ClearSCADA... so I'm not sure what you'd be planning to push back in.

 

ClearSCADA can 'import' data from a wide range of sources via its Drivers.  One of those is ODBC.. so you could have it retrieving the report data from your national headquarters ODBC-compliant database if you wanted.. Using the driver you would then get this data into separate points (i.e. it wouldn't be the same point as you're reading from the field devices), so that might work for you.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
AdamWoodland
Commander Commander
Commander
0 Likes
0
1289
nosaj
Ensign
Ensign
0 Likes
0
1280

Re: ClearSCADA: external data to Historian at regular intervals

Not a bad idea @BevanWeiss , but they're not in a position to do this. For better or worse, the data workflow from site to office is:

 

(collect data on site) -> (perform performance and reliability calcs on site) -> (export to head office: subset of ClearSCADA data, plus on-site calcs).

 

They're expecting not every point at headquarters, and they are absolutely expecting on-site calcs to appear with certain tags. The sites are variable enough that this makes sense. It might not be how I'd do it, but it's not insane and it's what I have to work with.

nosaj
Ensign
Ensign
0 Likes
0
1277

Re: ClearSCADA: external data to Historian at regular intervals

Thanks @geoffpatton for letting me know it's possible.

 

Other threads suggested that CDBHistoric is read-only to ODBC, and the error message I get simply says I'm not permitted to write to it. So I suspect it really can't be written to this way.