Comparison of Methods to Transfer Point Data Between Geo SCADA Systems

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Comparison of Methods to Transfer Point Data Between Geo SCADA Systems
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 09:38 AM
0 Likes
0
1792
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 09:38 AM

Comparison of Methods to Transfer Point Data Between Geo SCADA Systems

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 06:38 PM

📖 Home  Back  

 

When required to transfer data values between two Geo SCADA systems there are a number of options available, each with their own advantages and disadvantages. The table below acts as a guide to assist the design process when deciding the best option to choose.

  DNP3 EcoStruxture Web Services (EWS) OPC-DA OPC-XML-DA Sparkplug
Environment Description DNP3 slave running at one end, DNP3 master at the other; both components of the DNP3 driver EWS server enabled at one end, Advanced EWS client driver at the other OPC-DA client driver at one end, DBServer is inherently an OPC-DA server. Recommended to use the Advanced OPC driver in ClearSCADA if possible OPC-XML-DA client driver at one end, DBServer is inherently an OPC-XML-DA server Coming soon!
Available Target for Data Main server only Any Main or Standby server Any Main or Standby server Any Main or Standby server  
Data Addressing Method DNP3 point address as defined in the valuemap at the slave Database object's fullname and property Database object's fullname and property Database object's fullname and property  
Data Read Classes Current value, historical data and trends Current value, historical data and forecasts Current value only Current value only  
Data Read Efficiency Great, class 0, 1, 2, 3 polls and unsolicited Poor, only synchronous supported Great, asynchronous and synchronous supported Poor, only synchronous supported  
Bandwidth Requirements Low, binary protocol High, XML based data transfer Medium, binary protocol with transfer overhead High, XML based data transfer  
Low Latency Dependency Low, able to handle high latency, e.g. satellite, when configured with suitable timeouts Medium, http based High Medium, http based  
Controls Supported Yes Yes Yes Yes  
Method Calls Yes No No No  
File Transfer Yes No No No  
ClearSCADA Licence Requirements DNP3 driver included by default in the core licence No additional licence required. See footnote 1 OPC licence required OPC licence required  
Protocol Encryption None, could use external IPSec tunnels Use of https if configured AES tunnel when using DBClient to tunnel, when using DCOM dependent on DCOM configuration Use of https if configured  
Database Authentication Device based, DNP3Secure v2 supported Connection based, defined at the server for all connecting clients Defined at the client, using private security only None (not supported by OPC standard)  
Ease of Configuration and Maintenance Poor, lots of options to tweak, valuemaps to maintain Great, simple configuration options Good, simple configuration options, connectivity options when using DCOM can be problematic Great, simple configuration options  
Network Security Statically configured TCP or UDP connection Statically configured TCP connection Uses DCOM for dynamic port assignments, requires DCOM aware firewalls to secure better than any-any between IPs Statically configured TCP connection  
Network Analysis Support (e.g. DPI/NIDS/NIPS) Limited protocol support on specialist devices XML based protocol, able to be processed by most IT appliances Limited processing possible by specialist devices XML based protocol, able to be processed by most IT appliances  


Footnote 1 - In ClearSCADA 2017 R3, ClearSCADA 2017 R2 and ClearSCADA 2017 from build version 7013 (~15th March 2019) onwards ensures no WebX licence is consumed. Previous versions of ClearSCADA may consume a WebX licence under certain circumstances which may stop users successfully connecting.

The information provided above is for connecting two ClearSCADA 2017 R2 versions together. For earlier versions of ClearSCADA the information above should still be accurate should the required drivers be available. For connecting to non-ClearSCADA systems the information will depend on what protocols and functions are supported by the remote device and as such this table should not be used for that decision making


The use of terms such as 'Low', 'Medium', 'High', 'Poor', 'Good' and 'Great' are subjective and should act as a guide only. Additional research, such as review of the protocol and specific system testing should occur to identify and quantify any metrics for your system design

From a general point of guidance:

  • DNP3 is great for situations where connectivity between the systems is unreliable or poor, or where bandwidth cost is a significant consideration

 

  • OPC-DA is great for quick setups where connectivity availability is extremely high or where the current value is all that is required

 

  • EWS is a great general purpose option to transfer data in an easy to manage way and where security requirements may require third-party systems the ability to inspect the data

 

  • OPC-XML-DA has limited use in this scenario


Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore