Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Execute structured text program with pick param and pick type animation

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Execute structured text program with pick param and pick type animation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Tanquen
Tanquen
Explorer

Posted: ‎2020-10-05 06:29 PM . Last Modified: ‎2023-05-03 12:09 AM

0 Likes
2
3751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-05 06:29 PM . Last Modified: ‎2023-05-03 12:09 AM

Execute structured text program with pick param and pick type animation

The current application has two checkboxes, one to disable the tags alarm with the '?Digital.Disable' and one to set a PLC bit for that alarm with the '?Control&Value="1"'. They have some level alarms that were four separate alarms that they now want combined so that was easy enough to add a calculation digital point and disable the four alarms. Now just the calculation digital point goes into alarm when any of the four are true and the checkbox just disables the new calculation digital point.

 

Now I'm trying to figure out how to make the one check box toggle the four PLC bits. Working with buttons I know you can't just have a pick action method set four values at once so I made a structured text program to look at one of the bits and if it's true make them all faults if it's false make them all true. 

 

It's easy enough to make the pick action method with the structured text object selected and then the method set to execute and it works but for the life of me I can't figure out how to get it to work with the pick param and pick type animation. I know there's an execute method in the schema so I must have the syntax or the spelling or something wrong but it never does anything and it's really frustrating because the pick action keeps getting setup and it's confusing as to which ones actually working. The pick param and the pick type that you've configured under animations or the pick action that also looks like it's set up. I'm using pick type 5 and I think that should work with the execute method. I did try the others 17 and 19 and 20 and whatever and none of those work and they only seem to work with VB. Also the example for 19 makes it look like you can just put a message box command with a string and have it work and their example doesn't work.

 

So this works in a pick animation:

SCX:////CLogicSTProgram/...Tags DNP.Bioxide.Calcium Nitrate Tank 6701.Level SP.Toggle Rdy Tags

Untitled.jpg

 

 

But this don't work in a pick param animation:

 

"SCX:////CLogicSTProgram/...Tags DNP.Bioxide.Calcium Nitrate Tank 6701.Level SP.Toggle Rdy Tags"+'?Execute'

Labels
  • Labels:
  • Logic
  • Scripting
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Hardin4019
Hardin4019
Troubleshooter

Posted: ‎2020-10-07 06:00 AM . Last Modified: ‎2020-10-07 06:03 AM

1 Like
1
3727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-07 06:00 AM . Last Modified: ‎2020-10-07 06:03 AM

Drop the SCX:////CLogicSTProgram/ and try again. I did a test with PickType 5 and PickParam ".PickActionTest.ObjectLink"+'?Execute' that executes a ST that toggles an internal point form 0 to 1 and back. Worked like a champ. 

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Hardin4019
Hardin4019
Troubleshooter

Posted: ‎2020-10-07 06:00 AM . Last Modified: ‎2020-10-07 06:03 AM

1 Like
1
3728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-07 06:00 AM . Last Modified: ‎2020-10-07 06:03 AM

Drop the SCX:////CLogicSTProgram/ and try again. I did a test with PickType 5 and PickParam ".PickActionTest.ObjectLink"+'?Execute' that executes a ST that toggles an internal point form 0 to 1 and back. Worked like a champ. 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
Reply

Link copied. Please paste this link to share this article on your social media post.

Tanquen
Tanquen
Explorer

Posted: ‎2020-10-07 08:26 AM

In response to Hardin4019
0 Likes
0
3717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-07 08:26 AM

Thanks, I'm so confused as to the best way to go. Since I couldn't get that to work I ended up putting the check box inside the group with the rest of the tags and the structured text object. Now I just have to drag the checkbox onto the screen and it's already linked. I was trying to figure out a way to use parameters to have the checkbox on the screen and then drag the structure text object onto it. I think it's better having it already linked but now it's completely different than all the other check boxes. They sure don't make the syntax on any of the number of ways you can do stuff easy. I put the SCX prefix on there because it's on there in the pick action wizard so you would think it would be similar using the pick param. I was also missing the .objectlink.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore